Topband: RFI - and lots of it

Jim Brown jim at audiosystemsgroup.com
Fri Oct 30 14:15:06 EDT 2015


Yes, or where other premises grounds are tied together. Systems like 
Telco, CATV, satellite, even lightning rods if there are any, building 
steel if there is any.

73, Jim

On Fri,10/30/2015 11:03 AM, Dan Edward Dba East edwards wrote:
> 'central point' being my main service breaker box?
> it's a good distance away from any plumbing...
>   
>
>
>       On Friday, October 30, 2015 12:28 PM, Jim Brown <jim at audiosystemsgroup.com> wrote:
>     
>
>   No, that should be done at a central point in each premises, and only
> when the plumbing is metallic and conductive to the earth.
>
> 73, Jim
>
> On Fri,10/30/2015 9:58 AM, Dan Edward Dba East edwards wrote:
>> ok...another thing i've wondered about...
>> every bathroom and utility sink plus the kitchen have 120 vac outlet quite nearby..
>> should i tie the green a.c. wire to the plumbing at each?
>> w5xz
>>
>>    
>>
>>
>>        On Thursday, October 29, 2015 5:36 PM, Guy Olinger K2AV <k2av.guy at gmail.com> wrote:
>>      
>>
>>    It would really be something if in-the-slab copper was floating
>> electrically. I have seen the copper connected with a heavy wire out of the
>> slab connected to the ground bus in the main electrical panel. The other
>> end of the wire came up out of the slab next to the bonding point with the
>> copper pipe in a weather protected spot.
>>
>> If there is a question you should get a local licensed electrician who can
>> check it according to NEC + local practices. Local practices may specify
>> where and how the pipe is connected to the power ground.
>>
>> You might want to check if an ohmmeter shows a dead short between the
>> spicket copper pipe and the power ground.
>>
>> If it ain't connected, you need to get that fixed right away.
>>
>> 73, Guy K2AV
>>
>> On Thursday, October 29, 2015, Jim Brown <jim at audiosystemsgroup.com> wrote:
>>
>>> On Thu,10/29/2015 2:45 PM, Dan Edward Dba East edwards wrote:
>>>
>>>> all my plumbing is copper, hot and cold water, in the slab.  and, i have
>>>> an outside water spigot just a few feet away from my service
>>>> entrance...should I tie it in too ??
>>>>
>>> NEC REQUIRES that it be tied in.
>>>
>>> 73, Jim K9YC