[TowerTalk] tower grounding

K7LXC@aol.com K7LXC@aol.com
Sat, 13 Jun 1998 14:45:28 EDT


In a message dated 98-06-13 14:38:47 EDT, Brian.Harris@sv.sc.philips.com
writes:

> 1.  Is brazing recommended or is it better to silver solder?  Note: It's too
> 
>  late for cadwelding these joints.

     You should never solder anything. One event with subsequent heating and
the solder is all gone. Compression or exothermic (like CadWeld) are the only
NEC approved methods.
>  
>  3.  How deep should I bury the #6 radials?  Note: We have no heaving in 
> North Texas.

      I'd go 12-24 inches. You could check with your building department to
see what code is for reference and make a decision based on that.

Cheers,  Steve   K7LXC

--
FAQ on WWW:               http://www.contesting.com/towertalkfaq.html
Submissions:              towertalk@contesting.com
Administrative requests:  towertalk-REQUEST@contesting.com
Problems:                 owner-towertalk@contesting.com
Search:                   http://www.contesting.com/km9p/search.htm