> But is a good RF radial grounding system really "one of
the best lightning
> grounds you can get".  A raft of small wires might well be
a worse
> lightning ground than a few nice big wires or rods.  The
smaller wires may
> fuse with the lightning current.  Say you get a 20kA
strike and you've put
> in 60 wires. That's 300+ amps into each wire (if the
current divides
> equally, which it probably won't). 300 Amps is a ballpark
fusing current
> for AWG10 wire in air (admittedly, that doesn't take into
account the short
> duration of the lightning impulse, etc.)

Not that it means anything, but I've never seen a BC station
radial wire melted or any of my own, despite years and years
of strikes. I only use #16 radial wire, and often only 50-60
radials. This includes my 318 ft tower.

I've always considered multiple radials to be a very good
ground for lightning, and either that's correct or I've been
very lucky for the 35 years I've had towers over 130 ft
tall.

I have lost the shields of cables where they run between
large independent ground systems, mostly the shields of F6
or F59 size cables that use aluminum foil shields. In one
case the shield of 7/8th heliax where it ran between a tower
and the radial system. I really think that was caused by a
piece of old guy line lying on the coax and across the
radial buss.  Never have had ground radials melt, or hard
(not plumber's solder) silver soldered joints unsolder.

73 Tom