[TowerTalk] Low Inductance Ground Idea
Jim Lux
jimlux at earthlink.net
Thu May 13 12:28:48 EDT 2004
At 09:00 AM 5/13/2004 -0700, Wilson Lui wrote:
>Yes. As long as the metal is non ferrous.
>
>
>
>-----Original Message-----
>From: towertalk-bounces at contesting.com
>[mailto:towertalk-bounces at contesting.com] On Behalf Of GALE STEWARD
<snip>
> Later, it dawned on me
>that I should have used 3 inch copper instead of the 3
>inch PVC that I installed through the wall to bring my
>coax and control cables into my basement radio room.
>This would provide a low inductance path from the
>radio room to the outside ground system as well as
>providing a raceway for the various cables. I wish I'd
<snip>
Copper pipe is a wonderful material! Easier to get than copper bar, and
for RF, lower inductance for a given mass or cost (skin effect and all
that). If you get a good hot torch, soldering lugs to it, etc. is easy.
Interestingly, there are some recommendations that you'd actually want a
high inductance/lossy path from outside to inside for the shield, to
prevent "bad things" on the outside (i.e. lightning induced transients)
from propagating inside on the outside surface of the coax (or common mode
on a twisted pair). One suggestion is to run the cables through a length
of iron/steel pipe, just for this purpose.
Obviously, if you take a direct hit on the antenna (or a big transient is
imposed on the antenna from an adjacent hit), you're in trouble, because
the antenna and feed line is doing just what it's supposed to: carry
signals from the air to your rig.
However, if you're worried about transients carried in through sneak paths
(induced on the tower, or on the outside of the coax), then choking the
outside seems a good idea (somewhat like putting a string of ferrite beads
over the outside, or clamping a ferrite around the keyboard cable on a
computer), and iron pipe has a much higher transient handling capability
than ferrite beads.
One could also do the "shielded room approach" where you bond the coax (all
the way around, as in a bulkhead connector) to a metal plate in the wall,
which is then connected to ground by a low impedance connection. Here, the
induced potentials on the outside get conducted away just like with any
shielding scheme.
Something to bear in mind, brought up by Tom a couple weeks ago, is that
the transients you're trying to protect against might not be coming in
through your feedline, but through your power line, and if you do a good
job grounding the rig, then going through your rig might be the best path
for the transient to go from power line to earth.
I suppose then, the real question is why you'd want a low RF impedance
ground connection from your rig (inside the house) to earth ground (outside
the house)?
Presumably, the RF starts out on the "inside" of the box (your rig), and
stays on the inside of the coax until it gets to the antenna
feedpoint. Therefore, the ground from rig to earth shouldn't be carrying
any RF unless there's some radiated field coupling to the outside. In this
case, unless you are also wearing a low impedance ground strap (which is a
huge safety hazard), you'll be at RF voltage, and the rig will be at zero,
and there will be a net difference.
Now, if you're driving a long wire antenna with a single wire feedline,
sure, you need that low impedance RF connection to earth ground, because
it's the other side of the circuit, however, I suspect most of us use rigs
with coax connectors on them these days, and the RF ground point (i.e. the
shield of the coax), such as it is, is at the antenna feedpoint.
It might be true that in a real station, with lots of little boxes, some
with decent 3rd wire grounds, some without, some with unknown capacitive
coupling to external sources, that providing a "known good low impedance
connection" to a common point would be useful. For instance, a lot of
antenna tuners have no explicit grounding connection other than that
through the coax, and since no box is perfectly shielding, you could get RF
on the outside of the coax and the box could be hot relative to the rig.
I've certainly had the unpleasant experience of having racks of equipment
where the grounding was bad, so one rack floated up to 60-70 VAC relative
to a "good ground" just from capacitive coupling between AC line and the
equipment. This is not a good thing when you have low impedance electrodes
attached to your head and you touch the rack.
In reality though, solving the "hot chassis" problem with a "low impedance
ground strap from equipment to ground point" is a fix for another problem,
that of imbalance, insufficent shielding, or defective equipment grounding.
More information about the TowerTalk
mailing list