[TowerTalk] Grounding & Generator Questions
    Jim Lux 
    jimlux at earthlink.net
       
    Thu Aug  4 19:10:56 EDT 2005
    
    
  
At 01:42 PM 8/4/2005, Doug Rehman wrote:
>Actually, this is not that complicated...
>
>There are three wires coming from the power pole (two hots and the neutral).
>There are three wires coming from the generator (two hots and a neutral).
>There are three wires going to the breaker panel (two hots and a neutral).
>The transfer switch (UL accepted Generac transfer switch DESIGNED for
>EXACTLY this purpose and DESIGNED to work with the generator) connects the
>two hot leads from the breaker panel to either the two hot leads from the
>utility power pole or the two hot leads from the generator. The three
>neutral lines (utility, generator, breaker panel) are all bonded together
>inside the transfer switch box.
And does that generator have the neutral and ground separated internally? 
If it's designed for stationary use (i.e. it has no receptacles, and you 
wire it up inside conduit) then it probably does. If it's a generator that 
can be used for portable use, then perhaps not.
Such are the subtleties inherent in the generator grounding question.
>Since the transfer switch is BEFORE the breaker panel, it does not deal with
>the separate neutral and ground lines that appear within the breaker panel
>and house wiring...
>
>Perhaps to avoid the picking of nits, I should have simply asked the
>question: Is 2" metal conduit a reasonable material for connecting the
>ground at my power meter with the ground for my shack TO CREATE A SINGLE
>POINT GROUND???
>
>Doug
>K4DDR
>
>
>
>_______________________________________________
>
>See: http://www.mscomputer.com  for "Self Supporting Towers", "Wireless 
>Weather Stations", and lot's more.  Call Toll Free, 1-800-333-9041 with 
>any questions and ask for Sherman, W2FLA.
>
>_______________________________________________
>TowerTalk mailing list
>TowerTalk at contesting.com
>http://lists.contesting.com/mailman/listinfo/towertalk
    
    
More information about the TowerTalk
mailing list