>Anyone know what the resistivity per unit volume concrete
>is?
There is concrete that has enhanced conductivity (so that would probably
represent an upper bound on conductivity).. given as having resistivities
of 1-40 Ohm-cm
Another reference gives 30-90 Ohm-m resistivity, which is roughly
consistent with what IEEE Std 80-2000 (Grounding for AC substations) uses.
That standard gives Oven Dried concrete as 1E8 to 1E11 Ohm-cm and wet
(damp, not uncured) concrete as 21-100 Ohm-m (2100 to 10k Ohm-cm) (that's
10-50 mS/meter). Page 68 of that spec says "Buried in soil a concrete
block behaves as a semiconducting medium with a resistivity of 30-90
ohm-meter." and then goes on to talk about how, particularly in resistive
soils, concrete encased grounding is a good idea, because the concrete will
tend to have lower resistivity than the surrounding soil, which from a
fault current dissipation standpoint, is a good thing.
IEEE Std 80-2000 does give the short time current loading capacity for
concrete encased elctrodes based on multiplying the result from
Ollendorff's formula by 1.4 (Sure.. Ollendorff.. Yep, that'll be in the
technician question pool next year). But, they do give the formula in the
spec, as well as one from Fagan and Lee.
Here's something from the "Portland Cement Association"
http://www.cement.org/pdf_files/SN2457.pdf
58 pages of excruciating detail on the resistivity of concrete, with
details on corrosion, etc. mostly aimed at low frequency (as in electric
trains)
Ball park summary... concrete is about the same as soil, maybe a bit lower
conductivity (more akin to rock, which after all, is what it is). Depends a
lot on what aggregate was used (sandstone has high conductivity, fly ash low)
But, of course, for lightning discharges, what you really want is RF
properties...
http://www.ndt.net/article/ndtce03/papers/v078/v078.htm
gives some data that looks like epsilon is about 3-10 from 500 MHz to 2.5
GHz (and pretty flat). Conductivity is steadily decreasing with decreasing
frequency.. Call it 40 mS/meter at 500 MHz, 150 mS/meter at 2.5G
Then, there's this posting on a list in 1998
http://www.sowacs.com/archives/98-03/msg00023.html with the interesting
observation:
Hydrating concrete is shown to simulates the dielectric behaviour of soils of
different textures. Its dielectric spectrum from 10 MHz to 1 GHz illustrates
the effect of water binding (> 100 MHz) and the Maxwell-Wagner effect (< 100
MHz). Around 100 MHz concrete exhibits only small changes of the dielectric
properties; this is known to occur also for soils of different textures. The
compressive strength of concrete appears to be predictable from the electrical
permittivity at 20 MHz, due to the Maxwell-Wagner effect.
The following might be useful...especially since they're looking at 100
kHz to 40 MHz
Al-Qadi, et al.,"Dielectric Properties of Portland Cement Concrete at Low
Radio Frequencies" Journal of Materials in Civil Engineering, V7, #3, Aug
1995, p192-198
Abstract:This paper presents a nondestructive evaluation method to
characterize portland cement concrete (PCC) based on its dielectric
properties. The work reported is part of an ongoing study to develop a
nondestructive evaluation method for PCC structures using electromagnetic
waves. A custom-designed parallel setup with an HP 4195A Network/Spectrum
Analyzer was used to form the measurement system. A model was established
for the measurement system and a set of calibration standards was developed
for the system calibration. Six different PCC batches were cast and their
complex permittivity was measured over 28 days of moist curing, with an
average of four specimens per batch. The selected batches covered a
representative variation of water to cement ratio and two aggregate types
using Type I portland cement. The complex permittivity of PCC was evaluated
over a frequency range of 0.140 MHz. Preliminary measurements showed
significant changes in the real part of the dielectric constant versus the
curing time. However, the change in the loss tangent was less pronounced.
Significant differences were also observed in the dielectric properties of
PCC specimens due to mix-design parameters variations and curing state.