[TowerTalk] Grounding the tower..alternatives
ersmar at comcast.net
ersmar at comcast.net
Thu Jul 20 14:44:33 EDT 2006
JC:
I (and most others here on TowerTalk) would advise against placing copper tubing in intimate contact with galvanized steel. So that would eliminate your first suggested alternative.
I use Harger 222T connectors to fasten my #2 solid tinned copper ground wires to the legs of my Trylon tower (at factory-drilled holes.) I also use Harger #213T connectors to connect these same #2 wires to other places on the tower steel, like at the coax ground points at the top and bottom of the tower. These conenctors meet all the lightning specs you site in UL96. They provide 1.5 sqin of surface area in contact with the tower steel; they have two channels that can firmly grasp two ground wires for the spec'd 1.5 inch length; and they include a sharp point in each channel that pierces each ground wire to hold it in place. The connectors also include sets of grooves on the contact portion of the connector to permit drainage of rainwater away from the surface underneath the clamp.
I suggest you look into using either of these connector assemblies, including the <T> version - electroplated tin - to connect your TINNED copper tubing to the tower legs. Or you can squeeze the flattened copper tubing against a piece of stainless steel, which is held against the tower galvanized surface with a SS hose clamp. But this is a bit more complicated thatn the staightforward Harger clamps that are made for this purpose. Just make sure your tubing is at least #2 gauge in size - the minimum for Harger clamps.
73 de
Gene Smar AD3F
-------------- Original message ----------------------
From: "JC Smith" <jc-smith at comcast.net>
> I'm using copper tubing, run inside garden hose while above ground, for my
> tower grounding "straps." I usually do the same thing (flatten the ends and
> make large terminal lugs out of them), but where corrosion might be a
> problem, like on battery busses, I've been tinning the copper "terminals"
> with tin/lead solder. I'm wondering if this will be good for connection to
> the tower? I know there are terminals (bonding lugs) designed to make this
> connection. Looking at some of the catalogs it appears they are made of all
> sorts of metals. I see bronze, electro tin plated bronze, and aluminum
> (which is probably intended for aluminum wire). There are also
> electroplated tinned copper lugs and unplated copper flat strap clamps,
> which are designated as tower grounding components (Harger catalog). Banjo
> clamps of tinned bronze are also shown specifically for attachment to
> lattice towers. Surface area in contact with the tower and in contact with
> the conductor appears to be a primary consideration. UL 96 Standard for
> Lightning Protection Components says a minimum of 1.5 in. of conductor must
> be secured within the connector, and also that 1.5 in. of surface contact
> between conductor and ground rod is required. Obviously, bonding surface
> area between the lug and the tower is important but I didn't see a minimum
> specified.
>
> It wouldn't be too difficult to fold and crimp the ends of the copper tube
> so that it would fit inside these commercial terminals just like a heavy
> gauge wire would, but it seems to be a better connection to the tower if the
> intermediate piece (the lug) was eliminated and the ground strap (the copper
> tube) secured directly to the tower (better continuous conductor surface
> area and fewer mechanical connections). What does the collective wisdom
> here think? Attach the bare copper strap directly to the galvanized tower,
> attach the tinned strap directly to the tower, or use some sort of
> intermediate lug?
>
> Thanks & 73 - JC, K0HPS
>
>
> -----Original Message-----
> From: towertalk-bounces at contesting.com
> [mailto:towertalk-bounces at contesting.com]On Behalf Of Cqtestk4xs at aol.com
> Sent: Thursday, July 20, 2006 4:08 AM
> To: TOWERTALK at contesting.com
> Subject: Re: [TowerTalk] Grounding the tower..alternatives
>
> You need not go to the bother of flattening the hardline. You have the same
> surface area with it round or flattened...........................K4FMX
> ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
>
> The flattening of the hardline was only on the ends. This made it easier
> to
> put flat against the tower (with a thin layer of stainless to prevent
> corrosion) and against the ground rod.
>
> Bill K4XS
> _______________________________________________
>
>
>
> _______________________________________________
> TowerTalk mailing list
> TowerTalk at contesting.com
> http://lists.contesting.com/mailman/listinfo/towertalk
>
> _______________________________________________
>
>
>
> _______________________________________________
> TowerTalk mailing list
> TowerTalk at contesting.com
> http://lists.contesting.com/mailman/listinfo/towertalk
More information about the TowerTalk
mailing list