> Maybe I have misunderstood how the Polyphaser clamps are 
> intended to be used, but if I pass the copper strip between 
> the bolts and around one side of the nominally 5/8" ground 
> rod (actually approx. 1/32" shy), everything seems to clamp 
> together just fine. IOW, the clamp is clamping the copper 
> strap firmly *against* the ground rod
> 
> Alan NV8A
> 
> 
> On 07/24/06 08:54 am Brad Nowak wrote:
> 
> > I too found the strapping clamps too large for standard 5/8 
> in ground rods.
> > I did find that they work perfectly on 3/4 in ground rods 
> usually only 
> > available at industrial electric suppliers (only in 10' lengths I 
> > might add).  I didn't like using the shims of copper as it 
> was a real 
> > PITA trying to get everything aligned to tighten securely.
> 

You got it Alan, PolyPhaser states in their instructions for the clamp:

"If using other than PolyPhaser ground rods, copper strap may be cut and
used to shim the strap-to-rod clearance"

All connections should be cleaned and the proper copper joint compound used,
of course.

John W8JJW