After 23 years in the Electrical construction trade, I have dealt with this  
about million times ( or a bit less).
 
Make the conduit large, 2-3" is fine.  Pull all cables at once, but,  also 
pull a #12 THHN stranded wire in also. You can use this as a pull wire for  new 
installs. NEVER use rope for a pull line along with other cables, as it will  
rip insulation of other cables to hell. Use generous amounts of wire pulling  
compound ( wire soap ), it will dry, but will still lubricate.
 
Good luck!
 
73-Chuck KI9A