[TowerTalk] whole house surge protectors

Barry w2up3 at verizon.net
Wed Sep 19 16:52:43 EDT 2007


I had the ICE suppressor on my mains.  I had a lightning strike earlier 
this summer and the internal parts of the ICE box were fried.  The 
electrician who inspected the house and did some repairs said it 
probably saved us from much more extensive damage (radios, computer, 
VCRs, TVs, etc. were dead.)  He replaced it with a GE unit that has a 
quicker response time and greater Joule rating, and was more expensive
Barry W2UP.

John Elsik wrote:
> I have been reading this with great interest.  I am installing a ground system now.  I was going to use an I.C.E 330 for the AC mains (whole house).  Would that be adequate?  Something is better than nothing.  It looks like it is a shunt type also.
>  
> John wa5zup
>
>
>
>   
>> Date: Wed, 19 Sep 2007 10:34:55 -0700> From: jimlux at earthlink.net> To: towertalk at contesting.com> Subject: [TowerTalk] whole house surge protectors> > I've been doing a bit of browsing> Most of the whole house protectors are shunt mode (which, by the way, > can actually cause some problems, making things worse)> > Intermatic IG1240RC> Leviton 51120-1> Panamax gpp8005> Siemens various models> > etc.> > In any case, a shunt mode suppressor will also suppress transients > originating within the house.> > There is a case where they will be of less effectiveness.. if you have a > transient induced on the branch circuit between the panel and your load, > then the transient propagates both directions, and, depending on the > relative lengths of the wire, it will get to the load before it gets to > the clamp. Once the clamp goes into effect, an inverted transient gets > reflected back, so you can calculate the maximum width of the > unsuppressed pulse. (you could use something like 
>>     
>  2 ns/ft as a > propagation speed... so for a 100 ft run, with the transient induced > next to the load (or downstream from the load), you get half a > microsecond or so before the voltage is clamped.> > > If the transient is induced on a branch circuit other than the one your > load is on, the suppressor is between the transient source and your > load, so it would clamp the transient before it arrives at the load.> > If you put a point of use transient suppressor *with a higher voltage* > than the whole house protector, it will take care of the half > microsecond impulse before the whole house protector kicks in, and won't > have to absorb as much energy.> > FWIW, statistics show that most transient damage occurs from transients > originating outside the house, typically from a lightning strike or MV > line / LV line fault somewhere (MV = 10-30kV, LV = 120,240,480V). That > makes the rise time of the transient much slower (it's low pass filtered > by the power line), and als
>  o makes the whole house protector more > effective.> > In the event of a MV/LV short (the only kind of line transient I've had > personal experience with in Southern California.. we don't have much > lightning here), you've probably got a significant overvoltage that > lasts 8-10 milliseconds or longer (until the MV breaker trips or fuse > blows). You'd have to hope that the surge suppressor can hold on that > long without blowing its internal fuses. Or, ideally, it would short, > and trip your main breaker. Since most of these whole house protectors > have energy absorptions in the few kilojoule range, I'm not very > sanguine about their ability to protect against this kind of fault. > Figure the case of a 14.4kV feeder shorting to the 240V drop into your > house (this has actually happened to me). If the series impedance of > the feeder, through the drop, into the grounding system, is on the order > of an ohm or so, the fault current is around 10-20kA.> > If the surge prot
>  ector is based on an MOV, the 400V MOV is going to > dissipate about 4-8 MW, or, 4-8 kJ/millisecond. If it takes a half > cycle for the breaker to trip/fuse blow, that's 8 ms, and about 50kJ > (which is why things literally explode when this happens).> > A surge protector based on a spark gap, which, once it fires, has a much > lower clamping voltage, will dissipate less energy in the protector, so > has better survivability.> > _______________________________________________> > > > _______________________________________________> TowerTalk mailing list> TowerTalk at contesting.com> http://lists.contesting.com/mailman/listinfo/towertalk
> _______________________________________________
>
>
>