[TowerTalk] UL Warns of Countefeit Ground Rods
    jimlux 
    jimlux at earthlink.net
       
    Sun Dec  7 09:36:19 EST 2008
    
    
  
Roger (K8RI) wrote:
> 
> Larry & Karen wrote:
>> My wife, a EE/P.E. forwarded this to me just today.
>>
>> http://www.mikeholt.com:80/newsletters.php?action=display&letterID=644&email=kaatnip@qconline.com
>> _______________________________________________
>>
>>   
> I'm just wondering why would I care whether my ground system has real UL 
> rods or not.
At least in the 2005 code, there's no particular requirement for the rod 
to be UL (you can use pretty much any sort of metal you want, galvanized 
pipe, for instance). The copper cladding is for corrosion protection.
There are some sort of generic notes in the front pages about using 
listed components.
> And now days what would be the primary ground?  Neutral from the pole?  
> Neutral from the pole ties to the panel ground which ties to the ground 
> rods.  However neutral from the panel and grounds to the outlets are run 
> separate.
The "ground" is at the service entrance, where the "grounded" conductor 
(aka neutral) and the "grounding" conductor (green wire) are bonded.
The electrical safety ground(greenwire) is really more of a "equipment 
bonding" conductor (there's a move afoot to actually change the wording 
in the code to do away with "ground", since it's so confusing.. Maybe in 
the 2011 or 2014 code..)
The whole idea is to give a low enough impedance path from equipment 
back to panel so that if there is a line->case short, the breaker will 
trip. For this application, no earth ground is needed.
Limiting the "touch voltage" of the case (so if you're standing in bare 
feet, etc.) is a secondary goal.
As far as the actual "grounding electrode" goes.. the code (2005 and 
2008, for sure, maybe earlier.. I gave my 2002 book away) requires a 
Ufer ground.
---
One potential issue with counterfeits is that they *might* corrode 
faster, and someone who was expecting a certain life from the rod 
wouldn't get that life.  (Of course, the crummy life of ground rods in 
general is part of why the code doesn't allow them as the primary ground 
connection means any more)
Could also make life interesting in the event of a lawsuit where, for 
some reason, the ground rod becomes at issue.  Who's liable here? (it 
probably depends on whether you're in a strict liability state or not)
Jim
    
    
More information about the TowerTalk
mailing list