Grounding for what purpose?
NEC safety (i.e. if something shorts to it)?
Lightning protection?
RF ground (i.e. it's part of a vertical antenna installation)?
These all have different objectives and ways to get there.
In general, some sort of concrete encased grounding electrode ("Ufer
ground") will meet the first. 20 feet of suitably sized copper wire
embedded in the concrete base does the trick and provides a handy way to
connect to it. (The tower bolts and rebar cage can also work, too.)
A bigger wire version of the electrical code ground will go a long way
towards meeting the lightning protection requirement, depending on what
you want to protect against (i.e. the run of the mill 10-20kA strike, or
the 99% percentile 300kA monster stroke), what is connected to stuff on
the tower, and what sort of voltage rise you can tolerate at the base of
the tower. Also, lightning protection is like insurance.. you have to
decide what you can tolerate in terms of failures/equipment damage
versus the cost and sophistication of the installation. If it's a
commercial 99.999% available 24/7 facility with huge consequences if
you're down, it's a very different matter than a ham installation where
you've got insurance to replace the gear and can tolerate a several week
wait for the new gear to come in the mail.
For RF ground, nothing beats a radial field of some sort.
Jim, W6RMK
>