I have a SPG question which I would like advice on.

Background:
There are four structures on my property; the newly built main house, 
about 1 1/2 years old; a separate garage with living quarters above, 
about 6 years old; a workshop whose electricity comes from the panel in 
the garage and has its own sub panel, and a radio tower. The main house 
and garage have separate electrical service feeds and meters which 
ultimately connect to the same utility company transformer which has no 
other connections. Connections to all structures are via underground 
conduit including utilities and CATV. The main house and garage are on a 
security system which connects between the two buildings via conduit. 
CATV also runs from the main house to the garage through conduit.

The main house has a single point ground consisting of a U shaped copper 
wire Cadwelded to 4 or 5 ground rods, all of which is underground. One 
end of the U is the safety ground for the electrical service and the 
other enters the building foundation about 25 feet away and is connected 
to an aluminum strip which is the station ground. All radio equipment 
and computers are connected to this ground. At the electrical service 
entrance there is a large, heavy aluminum plate connected to the service 
ground. Coax, control lines and AC to the tower each run in their own 
conduit, all of which terminate near the ground plate. The AC lines are 
completely enclosed and connect to the supply. The other conduits end at 
the foundation wall and all cables run through lightning arrestors 
bolted to the aluminum plate. The CATV hardline also enters at this 
point in its own conduit but it is not connected to the ground inside 
the building.

The garage does not have its own safety ground. It has a copper water 
supply and the service neutral is connected to the water lines. The 
water lines are fed by a plastic pipe from the well, i.e. no connection 
to the earth. The ground here seems to depend on the electrical system 
ground at the pole transformer and meters which are about 300 feet from 
either building.

The workshop does not have its own safety ground.

The tower is grounded at each leg by a heavy copper wire which runs 
horizontally about a foot below ground for about twenty feet. I think 
one of the legs has two wires so there may actually be four ground 
wires. There is also a ground rod next to the concrete base connected to 
heavy copper wire which runs up to a PVC box and connects to a metal 
plate. All cables from the antennas run through Alpha Delta lightning 
protectors which are connected to the metal plate. All control wires run 
to Polyphaser surge protectors which are grounded to the metal plate at 
its connection to the ground wire. All cables run underground about 300 
feet to the house.

Problem:
Lightning recently hit a tree about 400 feet from the house. Electrical, 
telephone and CATV lines run on poles about thirty feet away from this 
tree. The resulting surge did the following: damaged the CATV lines 
along the road (blew lots of fuses and melted several connectors); 
destroyed the cable modem and router in the main house; destroyed the 
master board of the security system in the main house; damaged the 
auxiliary security board in the garage (still waiting for an assessment 
of this damage but it's probably fried); popped most of the GFI outlets 
in the garage and destroyed the master CCTV controller in the main house 
and one of the CCTV cameras attached to the garage; destroyed two of 
three air conditioning thermostats in the main house which are connected 
to the security system for remote control purposes; destroyed a CATV 
amplifier in the garage. No radio or PC equipment was damaged except for 
an Elecraft band decoder and a brand new Green Heron rotator controller, 
both of which were connected to lines that were supposed to be 
protected. The Green Heron damage was minimal and has been repaired and 
I have yet to figure out how to fix the band decoder. There was no 
damage to any other electronics in either building.

Questions:
Based on the damage, my assessment is that an electrical surge probably 
hit the the main house and garage at the same time. The SPG in the main 
house worked like it should have but the lack of SPG in the garage 
caused the surge to find the path of least resistance through the 
security system and CCTV links, destroying them. The cable modem and 
router were probably destroyed directly by the surge on the CATV system.

To prevent these problems in the future, I think the CATV hardline 
should be grounded where it enters. This is easy but probably won't stop 
any surge on the inner conductor. What can be done for that?

Adding a SPG will help dissipate surges in the garage, but I am 
concerned that there may still be a voltage differential between the 
structures in case of another strike, which could cause similar damage. 
My vote would be to connect the SPG of each building together with heavy 
copper wire and ground rods externally underground but this would entail 
a run of some 125-150 feet of heavy copper and lots of digging. It is 
not possible to get to the SPG of the main house without a large amount 
of damage to landscaping. The other alternative might be to run a heavy 
cable through a spare conduit between the two buildings to connect their 
grounds together but I am uneasy with this approach.

Do I need to connect the two buildings? If so, would a cable through the 
conduit be safe? Any other suggestions?