[TowerTalk] grounding quesitons: Ufer, strap, exothermic welds
Dick Green WC1M
wc1m73 at gmail.com
Sun Apr 17 20:09:43 PDT 2011
I don't agree about not connecting to the rebar. That's the standard way to
do a Ufer ground and I believe that's the way it's described in the NEC. My
local jurisdiction required a visual inspection to verify the rebar
connections before the concrete was poured.
I would use standard ground rod clamps to attach the ground wire to the
rebar. It's a no-no to weld rebar unless you use special rebar made for that
purpose. That's why rebar is normally just wired together to form the cage.
But I don't know if that restriction applies to exothermic welding. I
vaguely remember reading about special kits for exothermically welding wire
to rebar, but I'm not sure about that. Something you could research. Clamps
should be OK because little or no air will penetrate through the concrete to
corrode the connections. Also, you can coat them with conductive grease to
further reduce the chance of corrosion.
For redundancy and lower impedance, I would use more than one wire to
connect the rebar to the tower. I used three, one for each tower leg and
radial run. I tied the rebar, tower legs and radial ground wires together.
To do this, I cut three lengths of wire long enough to reach from a ground
rod a foot or two from the tower, through the side of the concrete base to
the rebar, and from there up through the concrete to each tower leg. Each
wire is exothermically welded to the ground rod (50' radials extend from
there out to a series of exothermically welded 8' ground rods spaced 16'
apart.) The middle of each Ufer wire is clamped to the rebar using standard
aluminum ground clamps coated with coppper paste. That's how the Ufer wires
are attached to the tower legs, too. I could have used two separate wires
for each connection, one connecting the radial system to the rebar and one
connecting the rebar to the tower, but the way I did it ensures that the
tower legs remain connected to the radial system even if there's a failure
in the connections to the rebar.
I do agree with Jim that you shouln't use use stranded wire. I believe the
standard for lightning ground is #2/0 solid. Not knowing this at the time, I
used #1/0 stranded wire. What happens is that corrosion forms in the spaces
between the conductors and they lose connectivity with each other. This is
plainly visible above the concrete. I'm not too worried about it because the
outer surface of the indivudual conductors are still connected at each end
of the wire, effectively providing multiple parallel connections. But those
conductors may or may not be touching each other anymore, and any inner
conductors are probably no longer connected at each end. I haven't measured
it, but I would guess the impedance is not as low as it would be if the
conductors were in full contact with each other. Given the size of the #1/0
conductors, though, I think the impedance is still pretty low.
73, Dick WC1M
-----Original Message-----
From: Jim W7RY [mailto:w7ry at inbox.com]
Sent: Sunday, April 17, 2011 10:58 AM
To: Mat Eshpeter; towertalk at contesting.com
Subject: Re: [TowerTalk] grounding quesitons: Ufer, strap, exothermic welds
I would put some #2AWG tinned solid in the foundation and not rely on the
rebar.
I have used a clamp type unit to clamp the copper strap to the ground rod.
If it's lightning your concerned with, I would not use strap. Stick with
#2AWG tinned bare copper, copper clad rods and exothermic attachment.
73
Jim W7RY
--------------------------------------------------
From: "Mat Eshpeter" <kk1c at live.com>
Sent: Sunday, April 17, 2011 7:24 AM
To: <towertalk at contesting.com>
Subject: [TowerTalk] grounding quesitons: Ufer, strap, exothermic welds
>
> I am about to pour concrete for the base of my HDX589 tower. I am going to
> go with a Ufer ground as well as the Polyphaser recommended eight 75'
> radials with multiple ground rods (8' rods every 16'). Location is on top
> of a 1600' ridge in WV and lightning is a very real concern. My QRZ web
> page gives a feel for the location.
>
> To build the Ufer ground, I am thinking about connecting a single bare 2/0
> stranded copper wire to the rebar. Questions:
> 1) is one enough?
> 2) how do I properly connect the copper to the rebar? Is exothermic weld
> the only way? Any problem with dissimilar metals?
> 3) how should the copper exit the base slab - above grade or below grade?
>
> Also, seems that copper strap is the preferred ground material for
> connecting rods together. Will 0.032" thick strap have significantly
> better longevity than 0.022" strap? I am refering to the strap sold by
> Georgia Copper. Copper is expensive and I don't want to invest in copper
> that won't add any value to my installation.
>
> Where can I find exothermic weld products to connect copper strap to 5/8"
> copper clad ground rods? I am exhausted reading Harger, Erico, Terraweld
> info, and can only find wire-to-ground rod products, no strap-to-rod
> products.
>
> 73
> Mat
> KK1C
>
>
>
>
> _______________________________________________
>
>
>
> _______________________________________________
> TowerTalk mailing list
> TowerTalk at contesting.com
> http://lists.contesting.com/mailman/listinfo/towertalk
>
>
>
> -----
> No virus found in this message.
> Checked by AVG - www.avg.com
> Version: 10.0.1321 / Virus Database: 1500/3578 - Release Date: 04/16/11
>
More information about the TowerTalk