[TowerTalk] Info/Advice re: Exothermic Welds
Jim Lux
jimlux at earthlink.net
Mon Aug 20 16:40:04 EDT 2012
On 8/20/12 10:54 AM, Art Greenberg wrote:
>
>
> I imagine that the single-shot mold might be faster to use but more
> expensive than a reusable mold. If each trench run is 100 feet and I use
> 10-foot ground rods spaced at 20 feet, that's a total of 12 ground rods to
> bond to including the existing electrical service ground.
It's not entirely clear why you would want to put a rod every 20 feet on
a buried conductor. The wire laying in the trench itself isn't a bad
ground conductor.
Some sort of grounding electrode at each end is probably what you want.
And for lightning ground, strap doesn't buy you much over round wire.
From a lightning standpoint, the inductance is what's important and the
inductance of strap and round wire is pretty similar. (AC resistance is
lower for strap, so if it's part of your radiating systems: e.g. a
vertical antenna ground system, then strap might make a difference)
" The entrance
panel will contain a grounding plate on which lightning arrestors are
located, and I'll run a ground wire (or a wide copper strap) from the
grounding plate to that ground system, and to my electrical service ground
rod. "
For this, wire is the way to go. The AC resistance isn't the dominant
thing to worry about.
Of course, if you've got a pile of strap for other reasons, then you
might want to use it.
I've seen schemes where people curl the strap up and braze it to another
conductor, or wrap the strap around something like copper pipe or AWG2
stranded, and braze/hard solder it.
More information about the TowerTalk