[TowerTalk] Urgent: Should solar panel array be grounded to station ground and/or house ground?

K8RI K8RI-on-TowerTalk at tm.net
Tue Oct 9 17:31:09 EDT 2012


On 10/9/2012 12:04 PM, Jim Brown wrote:
> On 10/9/2012 8:34 AM, John W wrote:
>> Hi Chas,
>> The current plan is this:
>> They are going to run a #8 ground stranded wire down from the rail
>> system, following the same route as the electric wires, attaching it
>> to the ground bar inside the load center subpanel up in the attic,

This sounds like they are treating it as just another circuit and 
appliance ground. If it ties into the panel then it has to be treated 
that way according to code. I don't think this is the best of safest way 
to treat this much metal stuck up in the air, but as an opinion,  I 
don't think codes have kept up with solar panels and external power sources.



>> then continuing from there down through the conduit to the ground bar
>> inside the outside safety disconnect box, which will be installed a
>> few feet above ground, and then continuing from there and attaching to
>> the ground bar of the main house panel where the electrical
>> connections are also being made.  Then relying on the ground from the
>> main house panel out to a ground rod or two.  (Not sure what the
>> builder has installed, it was 1998 and I wasn't here, but I'm going to
>> email him and see if he remembers.)
>> In addition to the above, for lightning protection, I am also having
>> them run a #6 stranded ground wire from the roof rail system straight
>> down the side of the house to a 5/8" 8' ground rod which I am about to
>> go and drive into the ground.
>> That rod will eventually get tied to my perimeter ground as well, once
>> I install it and the towers.
>
> Good.
>> My question now is:  How many feet away from the house foundation
>> should this rod be installed?
>
> First, don't stop with one rod. More is better.  As to spacing -- we
> would like the rod to see moist earth, which reduces the impedance to
> earth, so we want it exposed to rainfall, but we don't want to make the
> downlead any longer than necessary, so it's a compromise.
>

I agree with Jim, that you also need a ground for lightning protection.

73

Roger (K8RI)

> 73, Jim K9YC