Question:
None of the tower sections are Cadwelded. They are bolted together.
How is it that these bolts make an adequate lightning connection but one
"has" to Cadweld the ground wire to the tower at the base? Clearly the
sections have to carry as much current as the ground wire(s).
Maybe a dumb question but some explanation more in depth than "it's
code" is sought.
73 de Brian/K3KO
On 9/16/2012 18:44, K7LXC at aol.com wrote:
>> I always avoid mechanical ground connections for the primary grounding
> conductors - cadweld the conductors to the legs.
>
> Umm, good advice for big commercial type towers but Cadwelding to a
> Rohn 25G, 45G or 55G leg will blow a hole in it.
>
> Cheers,
> Steve K7LXC
>
>
-----