[TowerTalk] bonding to AC power box or inside fuse panel?

Jeff Blaine keepwalking188 at yahoo.com
Tue Jan 22 02:06:40 EST 2013


OK, some practical considerations then.

If I bond to the power meter on the exterior, they have what looks like a 
plastic conduit running down into the ground below grade.  So where do I 
hook on?  Drill holes and screw the strap into the box that holds the power 
meter, spearing some conductive grease over everything the best way?  Does 
not seem a very good idea.  I definitely cannot get to whatever ground rod 
they may have put below grade without busting concrete.

And on the inside, I can pull the panels off and get to the mains feed 
ground line.  Got to be careful.  Or is it enough to connect to the breaker 
box casing?  The connection between the casing and the "bus bar" for the 
ground is not what I would call lightning nuclear duty safe.

The housebuilder should have thought ahead 7 years and asked me about it 
before laying in the wires.  ha ha.

73/jeff/ac0c
www.ac0c.com
alpha-charlie-zero-charlie

-----Original Message----- 
From: Jim Brown
Sent: Tuesday, January 22, 2013 12:12 AM
To: towertalk at contesting.com
Subject: Re: [TowerTalk] bonding to AC power box or inside fuse panel?

On 1/21/2013 5:10 PM, Dick Green WC1M wrote:
> Some grounding decisions are not straightforward. For example, my AC and 
> telco services are on one side of the house and the station "single-point" 
> ground is on the other side of the house. It would have taken 150 feet of 
> low-inductance wire and at least 10 8-foot ground rods and Cadweld shots 
> to connect the ground systems outside the house. So I decided to bond them 
> together inside the house, using about 25 feet of 1/0 wire. Not the 
> recommended way to do it, but it my opinion a better way to ensure that 
> the ground systems are at the same potential.

Right. I have a similar situation with my shack.  I took a "belt plus
suspenders" approach -- I ran a bare #6 around the perimeter, bonding it
to rods by the power panel, at several points around the perimeter, and
more outside the shack. Inside the shack, I have thinwall steel conduit
(EMT) between the breaker panel (entrance) and outlets under my
operating desk, which are, of course, bonded to the panel. My coax panel
is between those outlets (at floor level) and the operating desk, and
I've added a bond between the desk, the antenna panel, and the conduit.

> Another example is bonding the tower ground to the single-point ground at 
> the house. My first tower farm is 265' from the house. Being new to tower 
> construction, I laid 265 feet of 1/0 ground wire in the trench running 
> between the two locations in order to bond the ground systems. This was 
> not cheap, to say the least (though it was before the big run up in copper 
> prices.) Later, I read an article by Polyphaser that said if the ground 
> systems are more than 75' apart it does no good to bond them -- the wire 
> inductance will be too high to make an effective connection. With this in 
> mind, when I installed my second tower system in a different location 220' 
> from the house, I did not run a separate ground wire. The Polyphaser 
> argument made sense to me.

Yes, it's good practice, solidly based on fundamental circuit concepts.
In fact, it's also good to add common mode ferrite chokes to the cables
running between the towers and the shack to minimize noise coupling.

73, Jim K9YC