[TowerTalk] Ground rod
    K8RI 
    K8RI-on-TowerTalk at tm.net
       
    Tue Jul 16 23:11:58 EDT 2013
    
    
  
On 7/16/2013 10:53 PM, Jim Lux wrote:
> On 7/16/13 5:45 PM, les wrote:
>> I am putting up a new tower and was wondering if the ground rod for it
>> can go through the concrete in the base or is it better to place it
>> outside the concrete base?
>> _
>
> you don't really need a "rod" into the base to make a good ground. A
> "concrete encased grounding electrode" (also known as a Ufer ground,
> after Herb Ufer, who invented them) has a lower resistance to "ground"
> than almost anything else you might come up with.
>
> To make a CEGR/Ufer what you do is either "bond" to the rebar cage or
> put 20 feet of suitable bare copper wire (AWG 4 or bigger) into the
> concrete arranged so it's reasonably spread out (e.g. burying a coil of
> copper wire doesn't do much good).
>
> Bonding to the rebar works if
> a) the rebar isn't the kind covered with an insulating coating
> b) you have a good way to bond to it
> c) the rebar is tied together reasonably tightly.
>
> Some ways that folks get the bond is by bringing a piece of the rebar up
> through the top of the concrete, and then using a suitable clamp to
> that. (that makes a bit of a challenge.. the clamp is then something you
> need to maintain).
Just CadWeld it
>
> THe other way is to run a copper wire down into the concrete and clamp
> it to the rebar. Again there's the whole "suitable clamp" thing,
> although once encased in concrete, it's not like the bolts will come loose.
>
> So that's why the most common Ufer ground is the 20 feet of AWG 4 in the
> concrete (wrapped around the rebar cage for instance.
>
My choice would be to use the *(large*concrete block as a UFER ground 
and add a bare copper wire network of ground rods like the broadcast 
stations do
This is an external ground with the wire network attached to each of the 
tower legs above the concrete and encompasses half my back yard.  Over 
Kill? Maybe, but I had the wire, ground rods, and one shot CadWelds. 
It's taken quite a few direct hits with no damage.
Anecdotal? yes, but so far, I've been lucky
73
Roger (K8RI)
>
> What is *really really* important is that NOTHING should penetrate the
> concrete/soil interface. No rebar sticking out of the side of the
> concrete below grade. No copper wires sticking out to bond to ground
> rods. No rods sticking out the bottom of the concrete.  Only concrete
> should be touching soil.
>
>
>
>
>
> _______________________________________________
>
>
>
> _______________________________________________
> TowerTalk mailing list
> TowerTalk at contesting.com
> http://lists.contesting.com/mailman/listinfo/towertalk
    
    
More information about the TowerTalk
mailing list