Agree that the Ufer wiki entry re "chip and flake" is soft. However, the
potential problems with buried copper or copper in concrete are well
documented/known issues, so I think the logic holds. I think the codes
tend to "get it right" over time and experience, and they support the
conclusion.
My IEEE membership doesn't include the groups with the papers of
interest so getting the references is expensive. However, I did find a
"public" powerpoint that may be of interest
http://ewh.ieee.org/r3/nashville/events/2011/Lightning%20Protection%2005-03-11.pdf
Jim, if you have institutional access to the IEEExplore library, would
you revise the wiki Ufer entry?
Grant KZ1W
On 7/18/2013 7:01 AM, Jim Lux wrote:
> On 7/18/13 6:29 AM, Grant Saviers wrote:
>> "extrapolation" may have been a poor word choice, but my reasoning is
>> that copper pipes are not buried without special precautions for
>> domestic water service because of corrosion. Another reason is that the
>> galvanic cells and/or stray currents that exist in soils can cause
>> electrolytic erosion. Copper clad ground rods are known to have finite
>> life, sometimes quite short in certain soils. Some concrete mixtures
>> were a disaster with buried radiant heating copper tubes and that
>> application now very rarely uses copper in concrete. There are
>> discussions on this reflector that AM broadcast station copper ground
>> screens disappear over time. Copper alloys in marine environments are
>> protected with sacrificial anodes or impressed voltage systems. Copper
>> in air lasts a long time, in an electrolytic or hostile chemical
>> environment not so.
>>
>> So, why expose a Ufer ground lead to what might be an environment that
>> significantly shortens its life, particularly if it isn't possible to
>> inspect it? As I have read the Ufer literature and codes, steel rebar
>> is the conductor, not buried copper wire, and the connection is to a
>> protected rebar exit point from the concrete.
>>
>> wikipedia re Ufer: "Ufer's original grounding scheme used copper encased
>> in concrete. However, the high pH of concrete often causes the copper to
>> chip and flake. For this reason, steel is often used instead of copper."
>>
>> see http://www.psihq.com/iread/ufergrnd.htm and
>> http://en.wikipedia.org/wiki/Ufer_ground
>>
>
> I'd be interested in seeing a reference for the "chip and flake"
>
> I'm not too impressed by the Wikipedia entry. For one thing, they
> don't cite Ufer's paper, nor any of the subsequent ones on the
> subject. And that comment about "flash into steam", as you can
> imagine from this discussion, is one that I would not agree with.
> Unfortunately, the cited reference is too general to actually find it.
>
>
> Ufer's original paper
> IEEE CP 61-978 (Conference Paper), Herbert G. Ufer
>
> Then there's all of these, among others..
>
>
> Herbert G. Ufer "Investigation of footing-type grounding electrodes
> for electrical installations" IEEE Trans. Power Apparatus and Systems,
> Vol. 83 p. 1042-1048 October 1964
>
> Fagan, E.J. and Lee, R.H. (July/August 1970). The Use of
> Concrete-encased Reinforcing Rods as Grounding Electrodes", IEEE
> Trans. on Industry and General Applications, Vol. IGA-6, No. 4, pp.
> 337-348
>
> Harding, G. and Harris C.A. (1970). Some Engineering Objections to
> Using Reinforcing Steel as Grounding Electrodes", IEEE IGA Conference
> Proceedings, pp. 181-187. Discussion by Lee, R.H.
>
> Preminger, Julius. (Nov./Dec. 1975). "Evaluation of Concrete-encased
> Electrodes", IEEE Trans. on Industry Applications, Vol. IA-11, No. 6,
> pp. 664-668.
>
> Kawai, M. (1965). "Studies of Tower Footing Resistance on Transmission
> Lines", IEEE Conference Paper No. 31 CP 65-704.
>
>> Grant KZ1W
>>
>> On 7/17/2013 6:26 PM, David Gilbert wrote:
>>>
>>> Why is that a "reasonable extrapolation"? Copper wire won't corrode,
>>> and rust/corrosion is the ONLY reason that codes require rebar to be
>>> fully embedded in the concrete. Please explain ...
>>>
>>> Dave AB7E
>>>
>>>
>>>
>>>
>>> On 7/17/2013 12:52 PM, Grant Saviers wrote:
>>>> Building codes now REQUIRE Ufer grounds in many jurisdictions for new
>>>> foundations. Codes also REQUIRE that rebar be covered with concrete,
>>>> usually a minimum of 3" to prevent corrosion ingress along the rods.
>>>> So it is reasonable to extrapolate that ground wires connected to the
>>>> rebar should not exit the concrete below grade ... <snip>
>>>>
>>>> Grant KZ1W
>>>
>>>
>>> _______________________________________________
>>>
>>>
>>>
>>> _______________________________________________
>>> TowerTalk mailing list
>>> TowerTalk at contesting.com
>>> http://lists.contesting.com/mailman/listinfo/towertalk
>>>
>>
>> _______________________________________________
>>
>>
>>
>> _______________________________________________
>> TowerTalk mailing list
>> TowerTalk at contesting.com
>> http://lists.contesting.com/mailman/listinfo/towertalk
>>
>
> _______________________________________________
>
>
>
> _______________________________________________
> TowerTalk mailing list
> TowerTalk at contesting.com
> http://lists.contesting.com/mailman/listinfo/towertalk
>
More information about the TowerTalk
mailing list