[TowerTalk] Challenging Grounding/Bonding Situation ?
Gary Schafer
garyschafer at largeriver.net
Fri Sep 12 21:22:58 EDT 2014
> -----Original Message-----
> From: TowerTalk [mailto:towertalk-bounces at contesting.com] On Behalf Of
> Jim Brown
> Sent: Friday, September 12, 2014 7:46 PM
> To: towertalk at contesting.com
> Subject: Re: [TowerTalk] Challenging Grounding/Bonding Situation ?
>
> On Fri,9/12/2014 5:27 PM, Gary Schafer wrote:
> > You only think that there is no ground between your house and
> shack/garage.
> > That neutral wire is serving both as ground and neutral between the
> two
> > buildings.
>
> I disagree with your analysis, and as I noted, the system I described is
> specifically listed as acceptable in the last code I bought, about 2003.
Maybe where you live the local board had not yet adopted the newer NEC code?
Current NEC code does not allow for only 3 wire feeds from one building to
another. They require 4 wires.
> Neutral and ground are two separate conductors.
Neutral and ground are the SAME conductor in your 3 wire feed system. You do
have the neutral bonded to the panel in the shack as well as at the house
don't you? If you do not you have no path for a breaker to trip in case of a
fault!
>
> You are also ignoring inductance between these points you want to bond.
Of course inductance of long runs is a problem with lightning. But the NEC
still requires all grounds to be bonded.
73
Gary K4FMX
>
> 73, Jim K9YC
>
>
> _______________________________________________
>
>
>
> _______________________________________________
> TowerTalk mailing list
> TowerTalk at contesting.com
> http://lists.contesting.com/mailman/listinfo/towertalk
More information about the TowerTalk
mailing list