On Fri,9/12/2014 6:50 PM, Gary Schafer wrote:
> If you have only a 3 wire feed system from your house to garage then you
> have to have that feed neutral wire bonded to the panel at both the house
> and at the garage. If you do not have it bonded to the panel at the garage
> then there is no path for a breaker to trip if there should be a fault of
> hot to ground on any appliance like Bill described.
How many times must I say it? Neutral MUST BE bonded in both buildings
if ground is not carried. They are treated as separate premises.
73, Jim K9YC