[TowerTalk] understanding ground resistance measurements
Grant Saviers
grants2 at pacbell.net
Wed Aug 12 13:18:09 EDT 2015
I'm using a clamp on ground resistance tester Duoyi DY1000A to measure
some new ground rods and Ufer grounds.
New ground rods driven into bone dry soil 8' x 5/8 rods, #6 to tower base
south 85 ohms
north 0.05 ohms since connection is a loop and rod end is buried
west 88 ohms
2x#6 Cu in 45' trench 8" deep 65 ohms (some watered soil)
Interpretation: as I understand how the instrument works, if I don't
have a very low resistance ground in the network, I am measuring the sum
of the resistances, or nearly so, of an isolated branch. So, it seems
likely that the actual ground rods are around 40 to 50 ohms each.
Old tower ufer measurements
east tower (18 yards concrete 6 x 10' x 8') 1.5 ohms, known wet
spot, water table was about 5' down in fine clay this time of year,
partially touching an abandoned septic tank
west tower (5x5x8) 16 ohms, didn't hit the water table with this
foundation
Interpretation: The difference is a bit surprising. For both
towers, the reference ground resistance is only coax braids and AC earth
return paths to the shop
Ufer rebar out of foundation near mains entrance (250' perimeter x 12"
wide down 16") 0.041ohms
three #4 connections from Ufer rebar to power panels 0.034, 0.009,
0.009 ohms
two exterior 8' ground rods to power panel 0.023, 0.024ohms
Intepretation: these all seem way too low, particularly the two
exterior ground rod measurements.
Ufer rebar out of foundation at radios
measures >1000 ohms, instrument overload. Not good as equipment is
bonded to the #4 wire so there is a return path through the AC earth wire
More information about the TowerTalk
mailing list