On 1/21/15 5:29 AM, Patrick Greenlee wrote:
> I have a triangular tower with legs on 14 ft centers, yes, 14 feet, not
> inches. I built it with three separate concrete foundations, one per
> leg. It is currently tilted over so one leg is not touching its
> concrete embedded mechanical connection/mount.
>
>
> Am I missing something? Will a simple ohm meter test give a reasonable
> measure of Ufer ground quality, sufficient to decide the question of
> whether or not multiple copper clad ground rods need to be installed and
> interconnected?
You need to use an AC source for the measurement: a DC source will cause
polarization and the reading will be low resistance at first and then
rise (think as if it were an electrolytic capacitor). The other thing is
that a typical solid state multimeter uses such low current/voltage that
you're going to see strange readings.
if you have something like a 12-24V AC transformer around (12.6V
filament transformer, landscape lighting, bell transformer), you can use
it: measure voltage and current, and you can go from there. You can
even use 110V (with an isolation transformer from the line, please!)
>
> Is it too much of a leap of faith or otherwise to assume the inter-leg
> resistance is an adequate predictor of tower mount to Mother Earth
> conductivity?
>
Nope.. that's pretty much how they do it.