[TowerTalk] Rotator Lightning Protection
Bry Carling AF4K
bcarling at cfl.rr.com
Sun May 17 09:03:04 EDT 2015
I guess the moral of this story is don't connect your phone line to your amplifier?
On 16 May 2015 at 17:26, Chuck Dietz wrote:
>
> I used to pull all plugs and disconnect all antennas but had a problem because I left the
> equipment grounded and strike came over phone line through an amplifier to ground. Now I have
> an equipment ground disconnect too.
> Chuck W5PR
>
> On Saturday, May 16, 2015, Bry Carling <bcarling at cfl.rr.com> wrote:
> My solution is to pull all AC plugs from the wall and disconnect all antennas whenever a
> storm is coming. That pretty much takes care of most problems.
>
> My ground system is going to be improved from the current setup but I'm not going to the
> kinds of extremes that some people have, and assuming that will be a perfect system of
> protection.
>
> Best regards - Brian Carling
> AF4K Crystals Co.
> 117 Sterling Pine St.
> Sanford, FL 32773
>
> Tel: +USA 321-262-5471
>
>
>
>
> > On May 15, 2015, at 9:11 PM, Roger (K8RI) on TT <K8RI-on-TowerTalk at tm.net> wrote:
> >
> > Having worked with literally thousands of MOV,s from little ones up to 50,000 Joul ratings,
> They will typically fail shorted, BUT I have seen many fail open. It depends on the power
> contained in the "final spike" that causes them to fail. From power line spikes and nearby
> lightening strikes the ODDS ARE it/they will fail shorted. If enough power/energy is
> contained in that final spike at failure time, it becomes likely they will fail open and that
> anything on that line will fail as well.
> >
> > Based on experience, you can expect the MOV to fail shorted and it will PROBABLY
> protect any electronic device connected to it. That being the case, the prop pitch motor will
> PROBABLY need some sort of "fail safe" to prevent over rotation.
> >
> > That's a lot of probables, but it's unfortunately a fact of life, leaving you playing the odds
> which favor the MOV failing shorted, but with no guarantee it will do so. If the MOV works
> as we all hope, then you will need some sort of "fail safe"
> >
> > Since the big ground system was installed my tower has been hit at least 7 times that can
> be verified with nothing disconnected and NO MOVs in the rotator lines. No damage was
> seen.
> >
> > I can not say the same for my computers and network. A nearby strike did nothing to
> either station, but it sure cost me a lot in network and computer damage. The CAT-5 lines
> go through protection at the UPS for each computer. The connectors were melted and the
> wire contacts welded together at one UPS. The router, 8 port switch and most NICs were
> shot!
> >
> > So, lightening and MOVs are a crap shoot. They will protect you from the smaller stuff,
> but cause other problems. They are unlikely to protect you from the larger stuff.
> >
> > In the end, I'd use them, plan on the MOVs failed as a short, and hope for the best There
> is no guarantee, but you have tilted the odds in your favor..
> >
> > 73
> >
> > Roger (K8RI)
> >
> > .
> >> On 5/15/2015 10:38 AM, Paul Christensen wrote:
> >> N4CC and I have finally completed our remote Internet station in Hilliard, FL. Probably
> half our time spent before and during construction was studying and implementing lightning
> abatement. Ground rings were created around each tower, and the communications
> shelter. All grounds, including the adjacent electrical service ground are brought together at
> an external ground bus (EGB). In total, 55+ ground rods are used with four rods each 24 ft.
> Lines are bonded at the top and bottom of the towers. We do not disconnect anything.
> Everything stays up and running 24/7 regardless of the WX.
> >>
> >> Poyphaser rotator MOV protection devices are installed at the base of each tower. At
> the EGB, we're using an Array Solutions model. In looking at all the failure modes, I missed
> one: If the MOV on the rotator return lead was to short to ground, it creates a disastrous
> situation where the prop pitch will turn freely beyond the electrical stop point. The MOSFET
> is controlled by a PWM circuit and the duty-cycle is what varies motor speed. A shorted
> MOV will cause the lines to break apart up the tower at the coax loop. The prop pitch would
> stop at nothing and keep turning. Do the MOVs in these units generally fail open or closed?
> >>
> >> We're using a pair of M2 PCX2800 controllers. To help protect the MOSFET device
> from a similar "short-to-ground failure" during a lightning event, I designed a circuit that
> engages a vacuum relay such that the MOSFET is only exposed to the outside world during
> rotation. It's not a 100% guarantee against MOSFET failure, but should help to mitigate
> damage. This is an add-on that's similar to what K7NV did with the Green Heron prop pitch
> controller model.
> >>
> >> Here's my thought for a potential fix: While another vacuum relay could be added on the
> +48V supply side to the prop pitches, I could isolate circuit ground from chassis ground on
> the secondary side of the controller's power transformer. The primary would still be safety
> protected and meet UL. Isolating circuit ground from chassis ground would inhibit rotator
> turning in the event of a MOV failure on the return line.
> >>
> >> Anyone been through this? I welcome comments on any better ways to manage this.
> >>
> >> Paul, W9AC
> >> _______________________________________________
> >>
> >>
> >>
> >> _______________________________________________
> >> TowerTalk mailing list
> >> TowerTalk at contesting.com
> >> http://lists.contesting.com/mailman/listinfo/towertalk
> >
> >
> > --
> >
> > 73
> >
> > Roger (K8RI)
> >
> >
> > ---
> > This email has been checked for viruses by Avast antivirus software.
> > http://www.avast.com
> >
> >
> > _______________________________________________
> >
> >
> >
> > _______________________________________________
> > TowerTalk mailing list
> > TowerTalk at contesting.com
> > http://lists.contesting.com/mailman/listinfo/towertalk
> _______________________________________________
>
>
>
> _______________________________________________
> TowerTalk mailing list
> TowerTalk at contesting.com
> http://lists.contesting.com/mailman/listinfo/towertalk
More information about the TowerTalk
mailing list