[TowerTalk] RF and AC Cables In Buried PVC
jimlux
jimlux at earthlink.net
Mon Apr 18 08:37:12 EDT 2016
On 4/17/16 6:17 PM, Tony wrote:
> All:
>
> I'm in the process of getting materials together to run both RF and AC
> service cables from the house to a shed. I was going to install separate
> schedule 80 PVC pipes, but before I do, I was wondering if it's possible
> to run both types of cable in the same pipe? Are there any drawbacks,
> safety or otherwise when running both through a single pipe?
You generally should not run "low voltage" circuits in the same conduit
as AC power (in fact, the electrical code prohibits it). The risk is of
the AC line shorting to the low voltage circuits: since low voltage
circuits are generally limited energy, they don't have over current
protection, safety bonding, etc., so a short might flow enough current
to start a fire or shock someone. (and, of course, blow up your
receiver and transmitter)
There are some techniques that would make it legal, but would require
more time to explain to the inspector than it would take to just lay the
second conduit in the same trench as the first one.
>
> The RF cables are for a VHF / UHF array - the AC cables will power the
> lighting inside the shed.
>
> Thanks,
>
> 73, Tony
> _______________________________________________
>
>
>
> _______________________________________________
> TowerTalk mailing list
> TowerTalk at contesting.com
> http://lists.contesting.com/mailman/listinfo/towertalk
More information about the TowerTalk
mailing list