On 5/7/16 8:51 PM, John Schumacher wrote:
> Hello all:
>
> I have a KF7P MetalWerks cable entrance panel (great panel) that I
> previously had mounted on the side of my brick house. I now have a house
> with vinyl siding. The hole for the cables to pass into the house is on
> the back of the panel. I want to properly mount this and drill and seal in
> such a way as to prevent leaks. I would appreciate any advice. I am going
> to put up a Windom, a 2/440 vertical and a Diamond Discone.
>
> Also, my new shack is on the second floor so any advice about lengths of
> ground wire would be appreciated. I have 2 inch copper strapping that I
> will be using to run a bond to the house electrical ground.
>
I'd use ordinary 12AWG house wire to bond to the house's grounding
system (electrical safety ground - green wire - third prong). It's not
carrying RF as part of your antenna (hopefully), so low AC resistance
isn't important.
Strap is used when you want low AC resistance for minimum loss, like
when connecting radial fields to a vertical antenna or in a tuning network.