[TowerTalk] Mot R36 related to NUMBER of installed ground rods

Steve Bookout steve at nr4m.com
Fri Nov 3 09:43:21 EDT 2017


Jeff,

You install ground rods until either your back hurts, your wallet hurts, 
or both.

I have six 'strings' of four rods each for a total of 24 rods per 
tower.  Installed them 16 feet apart, in a one foot wide trench so I 
would never trip over them.  All are cadwelded with #4 stranded copper 
and attached to tower legs with stainless steel shim stock and stainless 
steel hardware.

I am comfortable with this installation.

73 de Steve, NR4M

On 11/3/2017 1:10:AM, Jeff wrote:
> I’m laying out the ground rod scheme for the towers.
>
> As I look at Mot R56, it seems like about 45’ of rods gets you to the 5 ohm target based on one of the graphics they provide  That’s about 9 ground rods spread out in 3 legs each with 3 rods separated by 16’ assuming 8’ rods and average soil.
>
> While I realize more is better, how do you determine “enough” in the context of ground rod count?
>
> 73/jeff/ac0c
> www.ac0c.com
> alpha-charlie-zero-charlie
>