>"Another subtlety is the recent standards requirement for two hole
compression lugs plus antioxidant between surfaces for all bonding wire
terminations. I think the idea with two hole lugs is to prevent
loosening of a single bolt attachment from movement of the wire, not so
hard with 2 gauge wire."
I'm a firm believer in 2-hole lugs. With two bolts, it's impossible to
accidentally loosen the lug with a side hit. They should be used at every
opportunity when making a mechanical bonding connection, including
commercial radial plates.