Gentlemen,
Thank you for well considered input.
1) Mention was made of using twisted pair. Is that practical for 40 horsepower 
motors?
2) I recall from past board discussions the necessity of minimizing the 
distance between, and area encompassed by, power carrying conductors to reduce 
emissions.  Would someone please expound on that.
3) The motor controllers will be soft-starts rather than VFD's . Are there any 
special EMI considerations regarding soft-starts?
Thank you,
Scott
Sent via the Samsung Galaxy Note® II, an AT&T 4G LTE smartphone
<div>-------- Original message --------</div><div>From: Jim Brown <jim@audiosystemsgroup.com> 
</div><div>Date:07/12/2016  8:34 PM  (GMT-05:00) </div><div>To: rfi@contesting.com </div><div>Subject: Re: [RFI] 
Wiring practices to minimize emissions </div><div>
</div>On Tue,7/12/2016 11:13 AM, James Gordon Beattie, Jr. wrote:
im, et al,
Breaking DC paths with optical interfaces reduces inductive and
radiated emissions.
How do you use an optical interface in a circuit carrying 30A DC? Or
even 30A AC?
Further, twisted pairs are good, shielded twisted pairs properly
bonded and grounded are better.
That is NOT universally true. It depends greatly on shield construction.
If the shield is a robust copper braid, it can improve isolation. If,
however, the shield is foil with a drain wire twisted at the same rate
as the signal pair and closer to one of the signal conductors than the
other, the shield CAUSES differential-to-common mode conversion, which
causes the cable shield to radiate the differential signal.  Nearly all
currently manufactured "rack" cable has this defect, including those
made by Belden.
See Neil Muncy's landmark paper in JAES, June 1995. The essence of his
work is on my website, and I've contributed several papers of my own
extending his work.
73, Jim K9YC
_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi
_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi