The article does say what the cause of this crack was.  Here is what 
they said: 
 
"A word of caution: A Ufer ground consisting solely of the tower 
foundation is a bad idea. Lightning surges passing through the 
foundation can vaporize water in the concrete and damage the foundation 
through rapid expansion of steam. An example of this unfortunate event 
is shown in Figure 4. This particular tower had no earth electrode 
system, other than the leg foundations." 
 
Jerry, K4SAV 
 
 Jim Lux wrote: 
 
Paul Christensen wrote: 
 
What exploding concrete??  Back up your claim with real life validated
proof.  My experience has been the opposite.  
Doug
  
 
Want evidence?  See Figure 4 (and the text below it) in the link below: 
 
http://www.mikeholt.com/newsletters.php?action=display&letterID=407
  
 
The text says the only grounding was through the foundation and makes 
no mention of whether it was a properly constructed CEGR (i.e. 20 feet 
of conductor, etc.) 
 
Also, the picture does not show whether a structural failure occurred 
as a result of the lightning damage (the tower is still standing, 
after all), or whether that's just surface damage.  If it's a 1/8" 
deep crack in the surface and doesn't penetrate, who cares?  For all 
we know from the limited data in the article there was a prexisting 
crack in the concrete that was enlarged as a result of steam induced 
spalling. 
 
 Considering that Ufer did an awful lot of tests over the years, and 
subsequent researchers have also done a lot of tests, I think that if 
there actually was a realistic concern about spalling and exploding 
foundations it would have shown up in the reviewed literature (as 
opposed to in anecdotal reports or ground rod manufacturer sales 
literature).  I have no doubt that there are cases where there has 
been lightning damage, but I would suspect that those don't fit in the 
category of a proper concrete encased grounding electrode. For 
instance, the "3 2 foot J bolts in the top of the footing" used to 
bolt the tower mounting plate is probably NOT a suitable grounding 
connection. 
 
The article also sort of contradicts itself.  On the one hand it 
advocates external grounding systems, but then, it says that the 
external 20 rod grounding system showed an impedance of 150 ohms, but 
after bonding to the structural steel, the impedance dropped to 1 ohm. 
Sounds to me like the steel was a better ground than the rods. 
 
The article also mentions the "conduit as choke" thing, which I used 
to believe in, but subsequently have not seen a good analysis to show 
that it actually works, particularly for large surge currents, taking 
into account the magnetic saturation of the steel. 
 
 According to NFPA 780, Ufer grounding is generally satisfactory 
provided that it is not the only earth grounding mechanism and that 
the ground is brought out beyond the concrete encasement to make the 
earth connection.
  
 
Which section? (just curious.. I don't have my copy of 780 here) 
 
 Paul, W9AC 
 
 
 ------------------------------------------------------------------------ 
 
_______________________________________________ 
 
 
 
_______________________________________________ 
TowerTalk mailing list 
TowerTalk@contesting.com 
http://lists.contesting.com/mailman/listinfo/towertalk 
  
 
  
_______________________________________________
_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk
 
 |