41. Re: [Amps] TL922 Power Plugs (score: 1)
Author: "Paul Christensen" <w9ac@arrl.net>
Date: Wed, 4 Nov 2009 10:00:21 -0500
Gary, Pre-2008 NEC, that's allowable as long as there is no other metallic path between structures. It still appears to be an allowable exception on some existing wiring with conditions. Myself, I w
/archives//html/Amps/2009-11/msg00046.html (9,724 bytes)

42. Re: [Amps] TL922 Power Plugs (score: 1)
Author: "Mike McCarthy, W1NR" <lists@w1nr.net>
Date: Wed, 04 Nov 2009 10:10:25 -0500
Bonding the neutral to ground at the appliance is OK ONLY when it is fed with the old 3 wire system that has no neutral running from the service panel. These systems are grandfathered. It is NOT OK t
/archives//html/Amps/2009-11/msg00047.html (9,270 bytes)

43. Re: [Amps] TL922 Power Plugs (score: 1)
Author: "Paul Christensen" <w9ac@arrl.net>
Date: Wed, 4 Nov 2009 10:48:11 -0500
Carl, Assuming it's not an autotransformer, then it seems that Sec 250.24 may be applicable if the one or both of the stepping transformers are "outside," in which case the serving CT is grounded to
/archives//html/Amps/2009-11/msg00048.html (14,608 bytes)

44. Re: [Amps] TL922 Power Plugs (score: 1)
Author: "Gary Schafer" <garyschafer@comcast.net>
Date: Wed, 4 Nov 2009 10:36:44 -0600
I think that this falls under "separately derived power" like a generator would. When using an isolation transformer on a boat the secondary center tap of the transformer goes to the boats ground sys
/archives//html/Amps/2009-11/msg00049.html (14,445 bytes)

45. Re: [Amps] TL922 Power Plugs (score: 1)
Author: "Gary Schafer" <garyschafer@comcast.net>
Date: Wed, 4 Nov 2009 10:42:42 -0600
But in this case neutral and ground are one and the same and it IS ok to ground the cabinet of the dryer to a ground. Under the new code, with separate ground and neutral wires, it is correct that ne
/archives//html/Amps/2009-11/msg00050.html (10,376 bytes)

46. Re: [Amps] TL922 Power Plugs (score: 1)
Author: "Gary Schafer" <garyschafer@comcast.net>
Date: Wed, 4 Nov 2009 10:48:53 -0600
Agreed Paul. However that part of the code seems to be kind of a farce as you have a similar condition if you live in a city with houses side by side. Several houses may be fed from the same pole tr
/archives//html/Amps/2009-11/msg00051.html (10,572 bytes)

47. Re: [Amps] TL922 Power Plugs (score: 1)
Author: "Gary Schafer" <garyschafer@comcast.net>
Date: Wed, 4 Nov 2009 11:00:12 -0600
Not so. If the ground and neutral are strapped together the GFI will immediately trip out as the current thru the hot and neutral wires at the GFI will be unequal. A GFI does NOT require a ground in
/archives//html/Amps/2009-11/msg00052.html (11,765 bytes)

48. Re: [Amps] TL922 Power Plugs (score: 1)
Author: "Gary Schafer" <garyschafer@comcast.net>
Date: Wed, 4 Nov 2009 11:15:13 -0600
Actually the reason to ground the neutral somewhere in the system is to ensure that there is no potential difference between earth and neutral in this type of system. Once the neutral is grounded, as
/archives//html/Amps/2009-11/msg00053.html (12,079 bytes)

49. Re: [Amps] TL922 Power Plugs (score: 1)
Author: r391 <r391@worldnet.att.net>
Date: Wed, 04 Nov 2009 12:35:29 -0500
Afternoon Carl... A very long time ago I asked the plant electrician where I worked at the time about this very thing... now he told me that the the reason you don't bond in two different areas on th
/archives//html/Amps/2009-11/msg00054.html (14,565 bytes)

50. Re: [Amps] TL922 Power Plugs (score: 1)
Author: Roger <sub1@rogerhalstead.com>
Date: Wed, 04 Nov 2009 21:11:19 -0500
Ground Fault Interrupter? I say that only half jokingly as I'd bet that about 75% of the ham stations out there are in homes without GFIs. The average home in existence was built well before they wer
/archives//html/Amps/2009-11/msg00055.html (11,936 bytes)

51. Re: [Amps] TL922 Power Plugs (score: 1)
Author: "Paul Christensen" <w9ac@arrl.net>
Date: Wed, 4 Nov 2009 21:27:19 -0500
Not to confuse matters, but as of Jan 1, 2002, the NEC requires AFCI devices installed for bedroom receptacle outlets in new home construction. So, if the shack is located in the bedroom of a new ho
/archives//html/Amps/2009-11/msg00056.html (9,286 bytes)

52. Re: [Amps] TL922 Power Plugs (score: 1)
Author: Ron Youvan <ka4inm@tampabay.rr.com>
Date: Thu, 05 Nov 2009 02:49:39 +0000
We had one put in the bed room circuit at our farm house when we had the place re-wired last summer. Every time lightning strikes within 5 miles, the $21 breaker goes open. Lovely! -- Ron KA4INM - R
/archives//html/Amps/2009-11/msg00057.html (9,230 bytes)

53. Re: [Amps] TL922 Power Plugs (score: 1)
Author: jimsmitheguard-a@yahoo.com
Date: Wed, 4 Nov 2009 19:07:08 -0800 (PST)
Al, There is no need for a neutral in this case, however you should be concerned about using the proper cord, plug, and receptacle. Each NEMA configuration has unique electrical characteristics assoc
/archives//html/Amps/2009-11/msg00058.html (11,636 bytes)

54. Re: [Amps] TL922 Power Plugs (score: 1)
Author: jimsmitheguard-a@yahoo.com
Date: Wed, 4 Nov 2009 19:09:42 -0800 (PST)
Mark, The neutral and ground must be bonded together at the main panel as stated on the reflector many times. The ground, and neutral bus are often one in the same in a residential panel.   The detac
/archives//html/Amps/2009-11/msg00059.html (10,356 bytes)

55. Re: [Amps] TL922 Power Plugs (score: 1)
Author: jimsmitheguard-a@yahoo.com
Date: Wed, 4 Nov 2009 19:11:50 -0800 (PST)
Oh yes, it is a sick bird (ill eagle). The NEC, or a modified version of it  is law in most places. They may not send you to the big house, but you will likely pay a penalty if caught(for not taking
/archives//html/Amps/2009-11/msg00060.html (9,870 bytes)

56. Re: [Amps] TL922 Power Plugs (score: 1)
Author: jimsmitheguard-a@yahoo.com
Date: Wed, 4 Nov 2009 19:13:56 -0800 (PST)
Bill, Grounded conductors (neutrals) and grounding conductors (equipment grounds) follow different rules, are connected differently, may be sized differently, and sometimes follow different paths. Th
/archives//html/Amps/2009-11/msg00061.html (10,109 bytes)

57. Re: [Amps] TL922 Power Plugs (score: 1)
Author: "Mike" <noddy1211@sbcglobal.net>
Date: Wed, 4 Nov 2009 20:03:19 -0800
Strange Story, I thought that most stuff that is used outside like electric drills, edges and lawn mowers had to be double insulated for the last 30 years or so. --Original Message-- Bill, Grounded c
/archives//html/Amps/2009-11/msg00062.html (10,628 bytes)

58. Re: [Amps] TL922 Power Plugs (score: 1)
Author: "Alex Eban" <alexeban@gmail.com>
Date: Thu, 5 Nov 2009 09:15:10 +0200
This is true! The point to watch, in my opinion, is to take the branch out from the main panel BEFORE the GFI, if used. A local GFI can then be added at the remote location and the local ground strap
/archives//html/Amps/2009-11/msg00063.html (11,000 bytes)

59. Re: [Amps] TL922 Power Plugs (score: 1)
Author: "Jim Carr" <n7fcf@hctc.com>
Date: Thu, 5 Nov 2009 00:52:55 -0800
I spent my working life wireing and the later half as a state electrical inspector. I am a certified master electrician and national;y certified electrical inspector retired since 2000. reading some
/archives//html/Amps/2009-11/msg00064.html (12,231 bytes)

60. Re: [Amps] TL922 Power Plugs (score: 1)
Author: "Carl" <km1h@jeremy.mv.com>
Date: Thu, 5 Nov 2009 10:09:57 -0500
In NH the homeowner can do all his own wiring subject to inspection; this includes new construction. When I moved here in 1989 I added a huge addition to an 1830's farmhouse which I pretty much gutte
/archives//html/Amps/2009-11/msg00066.html (15,518 bytes)