Vic:

To do this empirically, you can find tables of DC resistance of wire @75 
degrees C per 1000 feet in the National Electrical Code (Chapter 9, Table 8 
1990 NEC for example). Here are some numbers for your scenario (assuming 16 
feet of copper wire):

#12 is 7.77 ohms per 1000 feet:  16*7.77/1000 = .124 ohms * 120 amps = 15 
volts .... real bad!  -number provided for fun :-)
#4 is 0.308 ohms per 1000 feet: 16*0.308/1000 = 0.0049 ohms * 120 amps = 
591 mV
#2 is 0.194 (blah blah...) = 372 mV
#00 is 0.0967 = 185 mV

etc....

Again, the values given are for wire @ 75C (assumes temperature rise and 
ambient).  You probably won't be subject to too much rise unless you're 
going to be running RTTY or you use something much smaller than #4 AWG.  By 
the way, aluminum conductors are typically 50% higher in resistance 
compared to the same length of copper conductors so be careful if you 
decide to use aluminum range/dryer/service entry cable!   You'd need a 
minimum of #2 if you do use aluminum.

Running real big wire doesn't buy you much past #4 copper in my opinion.

The NEC requirements for wire size take the typical length of branch 
circuits in to account when they specify the wire size for a given branch 
circuit breaker trip  current.  It is still up to the designer/installer to 
assure that the voltage drop of a given circuit is within acceptable norms 
(3-5% maximum on a branch circuit).  Bottom line is they won't let you go 
smaller than what their tables say for a given circuit, but you often have 
to go bigger if the circuit is long.

Hope this helps,

Bruce R. Knox W8GN
RF Applications, Inc.


-----Original Message-----
From:   Vic Rosenthal [SMTP:rakefet@rakefet.com]
Sent:   Wednesday, February 02, 2000 22:50
To:     Amps reflector
Subject:        [AMPS] Wire size


I'm going to power a solid state amp with about 120 amps of 13vdc.  I'll 
need
about 6-8 feet of wire to get from the PS to the amp.  What wire size 
should I
use?

73,
Vic, K2VCO
Fresno CA

--
FAQ on WWW:               http://www.contesting.com/ampsfaq.html
Submissions:              amps@contesting.com
Administrative requests:  amps-REQUEST@contesting.com
Problems:                 owner-amps@contesting.com
Search:                   http://www.contesting.com/km9p/search.htm


--
FAQ on WWW:               http://www.contesting.com/ampsfaq.html
Submissions:              amps@contesting.com
Administrative requests:  amps-REQUEST@contesting.com
Problems:                 owner-amps@contesting.com
Search:                   http://www.contesting.com/km9p/search.htm


<Prev in Thread] Current Thread [Next in Thread>