NEC quotes relevant to this discussion:

How things change. When "we" installed an underground service, in our area 3 ground rods were required, but they are in triangle "more-or-less" and only 3 feet apart. This was roughly 10 to 15 years ago. All are tied together with a single ground wire back to the common point at the entrance panel. So all ground systems tie to that commom point

Note: I don't know the size, but those ground rods appear to be 8' and no more than 5/16ths, or maybe 3/8ths inch. Although I hear, "don't do it" the shortest route from the station SPG is a direct line, under the house to the common point in the main panel. It was that compared to nearly a 100' run around the house. Typical rise time would allow a much higher voltage differential in the station by going around Vs going through.

Twice I have "dug up" the rods and both times the clamps were loose. The one time I replaced them. I've been tempted to replace them with a current setup and larger ground rods. I thought the mechanical connections were not to be buried, but I don't know the requirements back then. I "assume" it was OK as the installation was hooked up be the power company and inspected by the local inspector.

Since then we have "picked up an inspector" who worked as a union electrician. "Rumor-has-it" according to a number of people in the area it's difficult to get him to OK anything that was not done by a licensed electrician even if it is perfect.

  73

Roger (K8RI)


Not less than two driven ground rods placed at a minimum of 6 feet
apart when a non-metallic water piping system exists or is to be installed.

A separate grounding conductor to each ground rod shall be utilized

The grounding electrode conductor shall be solid or stranded , sized in
accordance with the requirements of the NEC but shall in no case be less
than No. 6 AWG copper or No. 4 AWG aluminum or copper-clad aluminum.

All ground rods will be required to be minimum 1/2" x 8' copper weld or
5/8” x 8’ copper plated only.

No galvanized rods or piping will be accepted as a grounding electrode.

73
Frank
W3LPL



----- Original Message -----

From: "Donald W. Kane via RFI" <rfi@contesting.com>
To: eedwards@oppd.com, rfi@contesting.com
Sent: Friday, January 16, 2015 1:23:03 AM
Subject: Re: [RFI] w7ekb & ground rods

NEC requires minimum 6 ft. between ground electrodes..for better
performance minimum 2X electrode length (e.g. 16 ft for 8 ft rods).

73
Don
WB2BEZ


In a message dated 1/15/2015 4:46:00 P.M. Eastern Standard Time,
eedwards@oppd.com writes:

Excellent point Jim. All services' grounds (AC, telephone, television,
internet and ham shack cable entry point & ham tower) must be bonded to a
single-point ground system. There's no limit on number of ground rods as long
as they're bonded (i.e. tied to the same grounding system). 8 foot ground
rods need to be within 16 ft of each other, but can be closer if needed to
shorten cable run to each service ground connection.

Couple more good references for grounding and bonding standards from
Motorola & Harris:
http://www.radioandtrunking.com/downloads/motorola/R56_2005_manual.pdf
http://www.repeater-builder.com/ge/lbi-library/t4618r3a.pdf

73, de ed -K0iL

_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi

_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi


---
This email has been checked for viruses by Avast antivirus software.
http://www.avast.com


_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi
<Prev in Thread] Current Thread [Next in Thread>