The copper coated rods eventually will deteriorate, I've found too.  After 
pulling them out I've found them speckled where the copper has eroded away and 
the base material shown.  I like the solid copper tubing as ground rods better, 
but they are not that easy to embed.  Use water to get them in the ground.  

Dale, k9vuj


On 16, Jan 2015, at 15:47, "EDWARDS, EDDIE J" <eedwards@oppd.com> wrote:

Frank,

You might know this since you have some tall towers up in the air.

Did the contradictions between NEC (copper ground rods) and EIA/TIA-222F 
(12.2.2-galvanized steel ground rods) ever get resolved?  At work we follow NEC 
on comm buildings and are forced to follow 222 on tower structures.

The only place we’ve actually used some new galvanized steel ground rods was on 
guy wire grounds on our 500 ft towers and only in the southeast part of 
Nebraska with the known soil problems for galvanic corrosion.  That was after 
an inspection we found 1.5 to 2 inch holes on 4 inch anchors and the copper 
rods almost totally gone.

73, de ed –K0iL

From: donovanf@starpower.net [mailto:donovanf@starpower.net]
Sent: Thursday, January 15, 2015 7:35 PM
To: rfi@contesting.com
Cc: EDWARDS, EDDIE J; DWKANEPE@aol.com
Subject: Re: [RFI] w7ekb & ground rods

NEC quotes relevant to this discussion:

Not less than two driven ground rods placed at a minimum of 6 feet
apart when a non-metallic water piping system exists or is to be installed.

A separate grounding conductor to each ground rod shall be utilized

The grounding electrode conductor shall be solid or stranded, sized in
accordance with the requirements of the NEC but shall in no case be less
than No. 6 AWG copper or No. 4 AWG aluminum or copper-clad aluminum.

All ground rods will be required to be minimum 1/2" x 8' copper weld or
5/8” x 8’ copper plated only.

No galvanized rods or piping will be accepted as a grounding electrode.

73
Frank
W3LPL



----------------------------------------------------------------------
This e-mail contains Omaha Public Power District's confidential and proprietary 
information and is for use only by the intended recipient.  Unless explicitly 
stated otherwise, this e-mail is not a contract offer, amendment, or 
acceptance.  If you are not the intended recipient you are notified that 
disclosing, copying, distributing or taking any action in reliance on the 
contents of this information is strictly prohibited.
_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi

_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi

<Prev in Thread] Current Thread [Next in Thread>