Rik, 

In quick scan couldn't find anything on NEC Article 250 supporting your 
statement.  Did you find anything in 250?  I only found a reference to "6 ft 
minimum" distance, but that might be old reference and depend on length of the 
ground rod.  This makes sense for NEC since it's worried more about AC 
electrical safety not RF grounding.  In comm buildings R56 calls for using both 
an underground ground ring/buss and bonded ground rods as a single system 
bonded together.

However, your statement about rods closer than twice the length being 
unproductive is true.  It is a waste of money and has little effect on ground 
resistance, but I doubt it does much harm if any overall.  And the "two-times 
length" maximum is also true.  

I'd rather have any and all above ground, bonding connections from/to each 
service (AC, cable TV, ham radio, telephone) as short of a run as possible to 
the earth (e.g. buried, bonded ground rods) even if that meant the 8 ft rods 
were only 6-8 ft apart.  This would be required for an RF single point ground 
system as I know it.

These are interesting NEC links for those with time on their hands:

http://www.necconnect.org/resource/?Id=1000027&Asset=c67370a9-8aa8-4606-a9c9-bb631a89c2e2
 

http://fyi.uwex.edu/mrec/files/2011/04/W4.-Biesterveld-NEC-grounding-MREC2010.pdf
 

73, de ed -K0iL

-----Original Message-----
From: RFI [mailto:rfi-bounces@contesting.com] On Behalf Of Rik van Riel
Sent: Saturday, January 17, 2015 11:09 AM
To: rfi@contesting.com
Subject: Re: [RFI] w7ekb & ground rods

-----BEGIN PGP SIGNED MESSAGE-----
Hash: SHA1

On 01/15/2015 04:45 PM, EDWARDS, EDDIE J wrote:

> Excellent point Jim.  All services' grounds (AC, telephone, 
> television, internet and ham shack cable entry point & ham tower) 
> must be bonded to a single-point ground system.  There's no limit
> on number of ground rods as long as they're bonded (i.e. tied to
> the same grounding system).  8 foot ground rods need to be within
> 16 ft of each other, but can be closer if needed to shorten cable
> run to each service ground connection.

I thought NEC specified the opposite, specifically that
ground rods had to be at least twice their length apart,
in order for each rod to have its own independent
connection to ground.

In other words, ground rods spaced closer together than
twice their length will not result in as large a reduction
in ground resistance as ground rods spaced the recommended
distance.
- -- 
All rights reversed.
_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi

----------------------------------------------------------------------
This e-mail contains Omaha Public Power District's confidential and proprietary 
information and is for use only by the intended recipient.  Unless explicitly 
stated otherwise, this e-mail is not a contract offer, amendment, or 
acceptance.  If you are not the intended recipient you are notified that 
disclosing, copying, distributing or taking any action in reliance on the 
contents of this information is strictly prohibited.
_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi

<Prev in Thread] Current Thread [Next in Thread>