At 06:42 AM 4/13/97 -0400, you wrote:
>Hello Hakan, I am still here. As you know I got alot of techni-blaa-blaa
>about the HV sag. Seems as though everything is in order here, but still
>have the problem,
Your problem is most likely on the primary side of the circuit. At the load
you
are drawing, you need a minimum of #4 wire between your breaker panel and the
radio, with no other devices sharing the same circuit. Your report of several
volts sag is too much. My sag here with a 45 amp draw is less than 1 volt!
If your run from the breaker box is short (less than 10 feet) you can drop
down
one wire size. My run is 7' here, using #6 wire.
(((73)))
Phil, K5PC
--