[AMPS] HV glitch resistor/fuse?

To: <amps@contesting.com>
Subject: [AMPS] HV glitch resistor/fuse?
From: km1h@juno.com (km1h @ juno.com)
Date: Wed, 10 Dec 1997 11:30:16 EST
On Tue, 9 Dec 1997 21:19:49 -0600 John Lyles <jtml@lanl.gov> writes:
>Hey,
>
>When you fuse a HVDC line, remember that when the fuse blows during a
>fault, that DC doesn't like to be interrupted. What I mean is that you 
>can
>sustain a nice long hot arc. I remember an experiment in college 
>(Virginia
>Tech probably had one of the last power engineering labs before all 
>the
>kids went digital) in which we had these motor generator sets, and 
>load
>banks. We'd rev up the motor, either in series or shunt field config, 
>and
>start adding load (resistors to the generator output). The switches 
>were
>merely open knife switches. Electrical engineering students had to be 
>smart
>and keep a hand in their pocket, and flip these little blades open or
>closed by the knob. The floors were made of wood blocks, elevated, to
>prevent killing someone. We called it the Frankenstein Lab. It 
>separated
>the 'men' from the 'boys' in engineering (sorry if there are females
>reading this, it's only a figure of speech!) school.
>
>OK so now you have the setup. I had my experiement really loaded up, 
>and i
>believe that the motor was series wired, such that the additional load
>caused the field current to increase, which increased the speed, which
>increased the current, you get the picture... This thing was 
>screaming, and
>the professor came rushing over to tell me to shut it off. I started 
>to
>lift the DC load with a knife switch. I don't remember the voltage, 
>but it
>may have been a hundred or so. The thing just sizzled and kept going, 
>with
>a nice 1 to 2 inch arc continued in space across from the contact to 
>blade.
>YIKES! Luckily someone pulled the main breaker, one of those spring 
>loaded
>arc-chute Westinghouse things that really looked like it was from Dr.
>Frankenstein's lair.


I would guess then that is why true HV fuses are 3 to 9" or so long, at
least the ones I have used up to 6KV.
Using a standard AG type fuse in the HV line would probably duplicate
your experiment. 


>-----------------
>
>I learned that large DC currents are hard to interrupt. Back to the 
>present:
>We have this 120 KV fuse here, that opens in case a bank of 7 
>klystrons
>faults. It separates the main power rectifier from the capacitor bank,
>which is something like 80-100 uF at 90 KV. The fuse is literally 4 
>feet
>long, and made by Maxwell in San Diego. It is like a big pipe, full of 
>sand
>and somekind of element. When it blows, the inside burns up the entire
>length, and the sand sort of melts around it.
>
>In another system, we have these 30 KV capacitors in parallel. We 
>learned
>the hard way in 1992, when one shorted and all the rest of them 
>(dozens)
>dumped their energy into the short. They had 5 Ohm 100 Watt wirewounds 
>in
>series with each cap. Every resistor exploded, not to mention having 
>the
>fire department, and a big mess of melted steel and oil. Since then, 
>we
>have designed a new type of HV fuse, that is spring loaded. It is 
>merely a
>#22 wire, suspended in a big 'grasshopper' spring, that keeps a piece 
>of
>this wire about 6 inches long, under tension. It the capacitor were to
>rupture and short, the wire vaporizes, the spring rips it open, and 
>breaks
>the arc. It is helped by a carborundum (now Cesiwid) resistor of a few 
>ohms
>in series. We have tested it, and it saves the resistors, and isolates 
>the
>faulty capacitor. The grasshopper spring swings over and hits a ground 
>bus,
>another safe feature.

I worked as a part time test tech at High Voltage Engineering back in
'64-67 three nights a week after my regular job at National Radio.  The
DC supplies they built ranged from 100KV/200ma to 500KV @ 1A. Those big
supplies were 9'  tall and ran behind a 12" thick concrete door with
steel facing. When something let go the sound was awesome....not to say
the scattered remains of the PS section that went!
I do not remember what was used for fault protection.
I even got to play a bit with the 1 megavolt accellerator. 
 
>------------------
>
>Now, think about using a 3AG or one of those little Bussman fuses. 
>They are
>rated for 250 VAC, not much more. People have used them for HV power
>supplies for years, on the line side. When you use them on DC, and you 
>dump
>all that stored energy in an arc, that fuse will pop, but where does 
>the
>current go? it continues until the voltage is low enough to extinguish 
>the
>plasma. In this way, a plain fuse is not very good for fast breaking 
>the
>circuit during a big fault. Maybe a resistor (long, as someone 
>mentioned)
>is better, or a springy thingy, or a thin wire that goes poof.

A surge resistor with a long enough arc path and a small wire fuse link
would be close to ideal in a ham type amp. It fits 2 major requirements;
simple and cheap. It would have to be a smaller guage than the plate RFC
if it was to do its job. 

Which brings up another interesting question....Why doesnt the plate
choke open up during these Big Bangs?  A #28 wire should not survive if
the reasons we keep hearing are true. Food for thought.


 Has 
>anyone
>else figured out what the optimal fuse for a 3 to 5000 volt supply 
>would
>be?

The HV fuse from the motor generator set to the TBK transmitter aboard
ship was a 3KV/1A rating ( 5" long) for the 3KV @ 250ma of the 861 final.
The 1000V line to the VFO and driver 860's used a 1000V/250 ma fuse (3"
long) and ran 1000V @ 75 ma or so. I still have a few of them old fuses
here.
It appears that the Navy ran fuses at their rated voltages and 3-4 times
normal operating current. 

73  Carl  KM1H



>
>One more thing, during a tube arc, CPI/Eimac and Burle tubes typically
>suggested that the voltage in the arc is about 50 volts. Meaning that 
>the
>rest of your power supply voltage during the first instant of the arc 
>is
>across the series limiting resistor. You can use this to roughly 
>calculate
>the value of R, to keep the current below some specified limit. In the 
>big
>tuibes (yes, with handles), these methods are insufficient, and an 
>active
>crowbar, using an Ignitron or triggered spark gap, are manditory. Or 
>one of
>those fancy low-stored energy power supplies that we were chatting 
>about a
>few weeks ago here. We test the crowbar by dropping a #30 wire across 
>the
>output (with a vacuum HV switch under remote control). If the wire
>survives, then the crowbar is adequate to protect the few mil diameter 
>grid
>wires in the power tubes. This is the recommended test by the tube
>manufacturers. The TV transmitters have a built in crowbar and some 
>have a
>test wire as well. The crowbar is triggered by high current in the 
>power
>supply, usually from a shunt and a pulse transformer to step up the 
>voltage
>to fire the crowbar.
>
>73
>John
>K5PRO
>
>
>
>--
>FAQ on WWW:               http://www.contesting.com/ampfaq.html
>Submissions:              amps@contesting.com
>Administrative requests:  amps-REQUEST@contesting.com
>Problems:                 owner-amps@contesting.com
>Search:                   http://www.contesting.com/km9p/search.htm
>

--
FAQ on WWW:               http://www.contesting.com/ampfaq.html
Submissions:              amps@contesting.com
Administrative requests:  amps-REQUEST@contesting.com
Problems:                 owner-amps@contesting.com
Search:                   http://www.contesting.com/km9p/search.htm

<Prev in Thread] Current Thread [Next in Thread>