Commercially, what is usually done to protect thoriated-tungsten 
filaments (for tubes with handles) from excess inrush current is to 
limit the current to no more than 2 X the rated current at nominal 
operating voltage. This is specified in many CPI/Eimac data sheets. If 
you are designing from scratch, all this requires is to ask your 
filament transformer mfr to
make the transformer so that it current limits by magnetic design. This 
reliable approach is nearly universally used in broadcast and industrial 
RF systems with tubes, and is simpler than using PTCs, step start 
relays, triac ramp up, variacs, etc.

For really big tubes (tubes with lifting hooks) like the RCA/Burle 7835 
triode (with 96 filament bars, each carrying 75 amps) and Thomson/Thales 
tetrodes (TH781, TH558, TH526, TH628 for example) it is required to ramp 
up the filament from zero using a slowly increasing voltage (500 seconds 
typical), to allow the filament structure to mechanically adjust in 
length as it is heated, so as not to bulge & touch the nearby control 
grid. It is also important, on these tubes, to not apply any DC bias to 
the grid until the filament ramp is complete, so that if there is a 
momentary short, it doesn't connect filament potential to the bias power 
supply and damage supplies or spot weld the filament in this position. 
There is no such thing as instant on with these tubes except when there 
is a momentary power glitch that comes back within a few seconds, in 
which their filaments have enough thermal inertial to remain hot.

For the prototype power amplifier I am preparing to test in a few weeks, 
we just installed the filament cables. They are 1100 MCM cables, that 
are as thick as your wrist. They are 15 feet long to the power supply, 
which fills one equipment rack (20 kW filament). Tube damage from 
filament overcurrent is unacceptable in this case, as the tube costs 
more than a yearly salary or the cost of a home...

73
John
K5PRO