Re: [Amps] Fw: Re: 4 wire 240VAC service? What to do now?

To: "'Commander John'" <crazytvjohn@yahoo.com>, <amps@contesting.com>
Subject: Re: [Amps] Fw: Re: 4 wire 240VAC service? What to do now?
From: "Gary Schafer" <garyschafer@comcast.net>
Reply-to: garyschafer@comcast.net
Date: Mon, 4 Apr 2011 17:23:33 -0400
List-post: <amps@contesting.com">mailto:amps@contesting.com>
It makes no difference if they are both tied together at the outlet in your
case provided,, that is a straight run to the panel with no other outlets
along the way and the panel serving it is the main service entrance panel
and not a sub panel.

Note that sometimes a main panel is wired as a sub panel with the main
breaker located outside the house and the distribution panel located inside.
In this case the main breaker panel outside is your main service entrance
panel and the ground and neutral would be bonded there and not in the
distribution panel located inside.

The best thing to do with the neutral wire at the outlet if you are going to
use only the ground is to put a wire nut on the neutral wire and leave it.

73
Gary  K4FMX

> -----Original Message-----
> From: amps-bounces@contesting.com [mailto:amps-bounces@contesting.com]
> On Behalf Of Commander John
> Sent: Monday, April 04, 2011 4:35 PM
> To: amps@contesting.com
> Subject: [Amps] Fw: Re: 4 wire 240VAC service? What to do now?
> 
> 
> 
> 
> OK
> I have removed the bare neutral ground wire from the jack. It makes no
> difference considering they paralleled each other the whole length.
> I looked at the 41 page article as suggested.  Really, 41 pages.
> john W9ZY
> 
> ~~~~~~~~~~~~
> On 4/4/2011 8:26 AM, Commander John wrote:
> > I twisted the 2 grounds together and installed them in the center pin
> jack as it was that or cut one off.
> > Is there a better way?
> 
> PLEASE go back and STUDY what I  and several others have written several
> times in this thread, and in the power and grounding  tutorial that's on
> my website.  http://audiosystemsgroup.com/publish.htm
> 
> NEVER, EVER, connect NEUTRAL to GROUND at any point other than the point
> where it enters the building. The proper connections to your amplifier
> are the two 240V hot wires and the green wire. The neutral must NOT be
> connected.
> 
> 73, Jim K9YC
> _______________________________________________
> Amps mailing list
> Amps@contesting.com
> http://lists.contesting.com/mailman/listinfo/amps
> _______________________________________________
> Amps mailing list
> Amps@contesting.com
> http://lists.contesting.com/mailman/listinfo/amps

_______________________________________________
Amps mailing list
Amps@contesting.com
http://lists.contesting.com/mailman/listinfo/amps

<Prev in Thread] Current Thread [Next in Thread>