Gentlemen: 
If you are pushing for enhanced reliability in a Ham manufactured amp, run 
above its ratings, 
say a Heathkit SB 220, and focus on the  heat in the transformer being a power 
limiting, 
or a long term reliability factor, and since I would guess the the source of 
the heat, and probably 
the location of the highest  temps is deep in the center of the core 
laminations,  
could you significantly lower the transformer temp where it counts with 
external cooling 
fans on the transformer?   If the external core of the transformer under heavy 
Amp use, were
very hot to the touch, sort of "ouch, that's hot!"  with Pain threshold in 1/4 
second of fingertip contact,
how hot might that be, and say, if it was say, 190 F on the outside of the 
laminations, 
how much hotter is it likely to be on the inside center core?

Best Regards,   
Pat Barthelow, AA6EG

## per the various eng notes from pole pig and vault/plate xfmr makers,  the 
oil immersed
xfmr's  can have their rating's  increased  only marginally with external air 
cooling.   The dry 
types, which is what's normally used these days for vault step down 
transformers, and also
dry type plate xfmrs, the CCS rating's can be substantially increased with 
external air cooling..like
as much as  50%. 

## Most of them will also say the max internal temp, deep  inside the core, 
[spot temp] is typ
a good 10-20 deg C  hotter  than the external casing temp.  The theory is if 
you externally cool the
xfmr casing, the differential between the outside and deep  inside, increases, 
and allows for
greater heat transfer  from inside to outside.   You can spec max internal core 
temps however
you want. They just use a higher temp rated insulation inside them..for the 
insulation between turns,
and also the coating on the magnet wire/flat wire/buss bar strap used.  The 
lowest is typ 105 deg C
[ 55deg C temp rise over a 40 deg C  ambient temp.... + another 10 Deg C  for 
..'spot heating' . ]

## the xfmr could be outside , sitting in the blazing hot sun...or could be 
inside in the basement, where the
ambient may only be 15-25 deg C.  Then the specs just go up from there.    Like 
125 deg C rated units...
and the highest I have seen are 165 deg C rated units. [ 115 deg C rise over a 
40 deg C ambient + another
10 deg C for spot heating.  Some makers will allow  for  20 deg C..for spot 
heating. 

## before I retired last year, one of our 350 kva  dry type xfmrs  ran blazing 
hot, and was replaced with a 
450 kva unit.  We have provisions to constantly  measure the core temp, deep 
inside the xfmr..and also the outer
casings.  6 x 250 cfm papst fans, 6" diam variety  are used to cool it,   3 x 
down each side at the base of
the xfmr..on stand off bracket..with fans tiled at an  angle.   If it's a real 
hot day, and load is huge, the 6 x
fans  will kick in,, but that's  pretty rare.  If it gets way too hot, and 
exceeds a pre-set threshold, an alarm
goes off...and sent to the NOC.    The heat from the vault room is blown to the 
outside parking lot..
[which faces north]..and cool air on the north side replaces it. 

##  trying to get laminar airflow on an under-rated ham style plate xfmr might 
be a trick, but doable.  I'd opt
for a bigger xfmr, and be done with it, but that's not always feasible due to 
dimension constraints.  A fan will
work...provided you have room for it, and can tolerate the noise. 

later.... Jim   VE7RF 