back in the early 80s, APC was among the first to label SBS  ( StandBy Supply) as a UPS  ( UNINTERRUPTIBLE POWER SUPPLY ).... NOT !!!!!



some of the SBS units do some voltage regulation, before they go full battery.....   Dave 's explanation is great ,,,,

I bought a large EATON 2500VA  ( used on the bay)... it runs 24/365 running NY9H computers-radios & network and my OLED tv .on 119.9VAC .. keeping out utility surges ( my monitors say 135.3 during last week's windstorm ). Even provides heat in the winter.

bill    was a factory rep for APC in 82-83 when they started.


On 11/21/2020 1:05 PM, k1ttt.dave@gmail.com wrote:
It will depend on the ups and the amount of the dip.  I am surprised a 
circulation pump would draw enough to drop the voltage that much, usually they 
are relatively small.  Is the ups on the same circuit as the pump??  Assuming 
they are on the same circuit have you checked for loose or corroded connection 
from the breaker to the pump and outlet??

When you say the sdr is powered from the computer, is that via usb?  Or off one 
of the other power supply voltages internally??  Usually usb is pretty well 
regulated by itself so again it would surprise me that the line voltage would 
affect it that much.  If its off one of the other voltages then maybe a line 
drop would affect it, but that goes back to the paragraph above.

On the ups side.  Some ups's run full time and protect against voltage dips, 
others take some time to switch on and support voltage dips like that.  There 
may also be an adjustment in hardware or software for the switch over to 
battery point.  Some ups's also have a delay before they switch to battery so 
they may not pick up in time.

If you have an appropriate meter you might want to measure the dip to quantify 
it.  It could also be the pump is going bad and drawing way too much starting 
current.  Or another possibility is a faulty neutral between the house and 
pole, that can cause all sorts of nasty voltage swings and has been know to 
blow out equipment and cause fires.

David Robbins K1TTT
e-mail: mailto:k1ttt@arrl.net
web: http://wiki.k1ttt.net
AR-Cluster node: telnet://k1ttt.net:7373


-----Original Message-----
From: RFI <rfi-bounces+k1ttt=arrl.net@contesting.com> On Behalf Of Ron 
Hunsicker via RFI
Sent: Saturday, November 21, 2020 12:32
To: rfi@contesting.com
Subject: [RFI] Motor starting and UPS

Hello,

The power to my computer is via a UPS.  My SDR is powered from the computer.

When one of the water circulation pumps for my heating systems starts (an old 
B&G), the voltage dips so much that it is apparent in the waterfall and a 
drop/loss of audio.

I've tried switching legs (red v black) but that didn't help. Let's ignore the 
idea that the service is too small.

I thought that UPS might "protect" against such dips in the voltage and am 
(obviously) surprised that it does not.

Whadaya think?


Ron

--
Ron Hunsicker
1238 Cleveland Avenue
Wyomissing, PA 19610-2102
610-478-0371
ronhunsi at ptd dot net


*"Democracy dies in darkness"***
_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi

_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi

--
This email has been checked for viruses by Avast antivirus software.
https://www.avast.com/antivirus

_______________________________________________
RFI mailing list
RFI@contesting.com
http://lists.contesting.com/mailman/listinfo/rfi
<Prev in Thread] Current Thread [Next in Thread>