Lightning - NEC - Grounding
After going to "school" to receive training on the "National Electrical Code"
and "Lightning and Protective Grounding", I came home and immediately did the
following to my home electrical system and and ham shack;
1) made sure the main distribution panel (primary electrical breaker box) had a
bond between the neutral and ground. 2) made sure the ground lug of the breaker
panel was bonded to both the outside "driven" ground rod and the cold water
pipe. (no water meter and the well water supply runs in PVC, the well casing is
PVC, but the 220 VAC submersible pump is 150' below ground surface with 50' of
water above it) 3) I put a 8 foot copper clad ground rod in each basement sump
hole, bonded them together with bare # 10 copper and also bonded them to the
cold water pipe. 4) added a grounding conductor between the sump hole ground
rod in the basement shack and the electrical outlets ground (third wire,
mechanical ground) in the shack - the other end of course runs to the breaker
box with the phase and neutral conductors and terminates on the breaker box
ground lug. 5) ran heavy braid from the ground rod to each piece of radio
equipment with a ground lug. (3, 4, and 5 prevents potential differences
between the electrical panel ground, the chassis ground, and "earth" ground) 6)
the 50 foot Rohn 45 tower has a 8' ground rod at the bottom of the 3' hole
bonded to the tower legs. 7) the rotor mast at the tower top is bonded with old
Belden RG-8 cable to a ground rod driven near the tower base and the tower leg
the RG-8 runs down is also bonded to the driven ground rod. 8) the tower
grounds are bonded to the cold water pipes 9) the HV-2 is mounted on a 8' mast
driven into the septic leach field with about 1800 feet of 66' number 18 gauge
radials on the ground (the RG-8 type cable shield brings this ground to the
shack)
I have seen evidence (metal erosion at the highest point of the rotor mast)
that there has been static dissipation through the tower and station ground. I
try to make sure that all equipment is unplugged and the feedlines are
disconnected during storms (front end protection) but all ground connections
are left in place. Additionally I have not gotten around to disconnecting or
having a way to disconnect the HAM IV rotor cables from the the rotor control.
All the feedlines and the rotor cable run down the inside of the tower legs to
the ground surface. I believe that all aspects of my station wiring and home
electrical grounding is in compliance with the National Electrical Code. As
stated earlier, we do get lots of electrical storms here in this part of
Illinois, I've experienced a number of near by lightning strikes (less than a
quarter mile) but in the past fifteen years, the installation has either worked
or I've been very lucky.
73,
Gary - AB9M - www.csm-gh.com<http://www.csm-gh.com/>
----- Original Message -----
From: GARY HUBER<mailto:glhuber@msn.com>
To: Discussion of Ten-Tec Equipment<mailto:tentec@contesting.com>
Sent: Friday, July 01, 2005 11:22 PM
Subject: Re: [TenTec] OT: Lightning and Grounds
While I don't have a current copy of the National Electrical Code in front of
me, it does (or at least did several years ago) call for the bonding of all
"grounds" on the premise. My training was in a course in "Grounding and
Lightning Protection" which was held in Florida. My former employer (a very
large, national insurance company) operates data centers, communications
equipment, and other sensitive electronic equipment in thousands of sites
around the US. The buildings range in size from old service (gas) stations, to
multi-story, multi-million square foot complexes. Many of their buildings have
air terminals, a ground ring, and some have ground mats in addition to the
requisite driven rods and water main bond.
The Corporate headquarters tower building roof top is 197 feet above ground
with air terminals. I operated both commercial and amateur radio equipment into
antennas extending more than 12 feet above the air terminals for more than
twenty years from that site with no adverse effects from lightning or static
dissipation.
For example, the N9PE DX Spider node operating on 144.91 uses a Kantronics
KPC-3 TNC, an Alinco DR-1200, 35 feet of half inch Heliax® and a VHF-UHF
Cushcraft Ringo. The antenna is mounted and bonded to building steel, the
feedline shield is bonded to building steel near the antenna, the feedline
penetrates the roof pan through a metallic sleeve (no bond which creates a high
impedance to any energy on the outside shield of the feedline) then it is
terminated on a Alpha Delta protector before the radio. The A-D protector is
bonded to a grounding plate attached to building steel (support column) and a
double run of 4 ought that terminates at the building ground mat 190 feet
below. The power to the radio and TNC are from a common 12 VDC supply, via a
small UPS, connected to a common 120 VAC circuit which uses building steel for
the "mechanical ground". This is a mid-west location with lots of lightning
but we've not had any equipment fail due to lightning for over twenty years.
The NEC philosophy seems to be "bond all your grounding conductors together
so there is no step voltage or voltage differential; use lots of grounding
rods, mats, pipes, rings but keep them bonded together; provide low impedance
(that's RF current folks) paths to ground for lightning with high impedance (to
the lightning) signal paths to your equipment." And finally if everything is
bonded together via the ground conductors, and everything rises in voltage at
the same time from a direct or near hit, no transit differential, no sparks, no
damage...... that's the theory and it does seem to work. Or maybe I was just
very lucky for twenty plus years.
73
Gary - AB9M -
www.csm-gh.com<http://www.csm-gh.com/<http://www.csm-gh.com<http://www.csm-gh.com/>>
----- Original Message -----
From: Robert & Linda McGraw
K4TAX<mailto:RMcGraw@Blomand.Net<mailto:RMcGraw@Blomand.Net>>
To: Tentec<mailto:tentec@contesting.com<mailto:tentec@contesting.com>>
Sent: Thursday, June 30, 2005 10:00 PM
Subject: Re: [TenTec] OT: Lightning and Grounds
Carl's comments are really the only really safe way to handle the issue.
However, in many cases, such as remote radio installations or repeater
installations the approach of disconnecting is not a reality. At the same
time, proper grounding is a reality. I strongly subscribe to the practice
that all grounds being served by a common electric service must be bonded
(connected) together.
Several have asked about why disconnecting the antennas and leaving the
ground connections caused a problem. Look at it this way as a simple test.
Start with 2 driven grounds say some 20 ft apart. Measure the resistance
between the two. Then connect the two driven grounds together with a piece
of #8 or larger copper and again measure the resistance between the two.
Well of course, the connection between the two connected together will have
a much much lower resistance. Now then, apply ohms law, E = I*R. You have
2 values of R to use, one without the bond wire and one with the bond wire.
You choose an arbitrary value of current "I", say 100 amps. What's the
voltage between the two grounds? Now, say your radio equipment is
connected
to one ground and the AC mains is the other. Thus without being bonded
together the difference in potential will be flowing from your radio
ground,
to your radio equipment through your 3rd pin ground or from the chassis to
the neutral via the power transformer insulation. Even though the
equipment
is off. Result: damage to the radio and if the surge is large enough,
damage to the house.
In the example above I will use a R value of 25 ohms for the resistance
value of the un-bonded grounds and an R value of 0.1 ohm for the bonded
system. In each case the current is 100 amps. The voltage between the two
un-bonded rods would be 2500 volts and for the bonded configuration the
voltage would be 10 volts. Which case would you prefer? Most power
transformers have a test voltage rating, primary to frame of 1500 volts.
For the comment of the power company not requiring a driven ground, I don't
think this complies with the NEC. Perhaps someone that is more familiar
with the NEC can contribute to the statement. To that end, some have said
to use the water line as long as it is metallic. Many houses use copper
inside but have plastic or PVC to the meter. No ground exists in this
configuration.
I realize that this is not really along the topic of Tentec radios, but
does
apply to Tentec radios and all other brands as well. Thanks to the
moderator for allowing the discussion and post. To that end, I have a nice
paper which I have presented at several conferences and has been published
in several journals. It deals with "Lightning Protection for the Home and
Station". It is free for the asking. It is in Microsoft Word format and
the file size is about 175K.
If you wish further dialogue on the subject contact me direct.
73
Bob, K4TAX
RMcGraw@Blomand.net<mailto:RMcGraw@Blomand.net<mailto:RMcGraw@Blomand.net<mailto:RMcGraw@Blomand.net>>
171 Grandview Dr.
Sparta, TN 38583
----- Original Message -----
From: "Carl Moreschi"
<n4py@earthlink.net<mailto:n4py@earthlink.net<mailto:n4py@earthlink.net<mailto:n4py@earthlink.net>>>
To: "Discussion of Ten-Tec Equipment"
<tentec@contesting.com<mailto:tentec@contesting.com<mailto:tentec@contesting.com<mailto:tentec@contesting.com>>>
Sent: Thursday, June 30, 2005 9:25 PM
Subject: Re: [TenTec] OT: Lightning and Grounds
>I completely disconnect all my equipment when a storm comes. That means
> disconnecting all my electronic equipment from the antennas, power, phone
> lines, and GROUND.
>
>
>
> Carl Moreschi N4PY
> Franklinton, NC
> ----- Original Message -----
> From: "John Rippey"
<w3uls@3n.net<mailto:w3uls@3n.net<mailto:w3uls@3n.net<mailto:w3uls@3n.net>>>
> To:
<tentec@contesting.com<mailto:tentec@contesting.com<mailto:tentec@contesting.com<mailto:tentec@contesting.com>>>
> Sent: Thursday, June 30, 2005 10:13 PM
> Subject: [TenTec] OT: Lightning and Grounds
>
>
>> K4TAX wrote:
>>
>> "George, I do hope you have those driven grounds bonded to the AC mains
>> ground and all other driven grounds around the property. Failure to do
>> so
>> will produce a step voltage between two different ground during a near-by
>> lightning strike. Equipment connected between the two different grounds
>> will then share the current flowing between the two different grounds.
> The
>> result is that one can observe extensive equipment damage or worse."
>>
>> 1. I've often wondered what would happend with a lightning strike nearby
>> and everything connected together (as at my QTH): coax feed line ground
>> block; phone; AC main; AC outlet strip for radios; radios' bus bar
>> ground.
>> This may be dumb, but why would not the electrical charge from lightning
>> come bounding into the shack via the common grounds? Disconnecting the
>> antenna leads at the radios does not seem to be a protection since the
>> radios' grounds are common with the outside grounds.
>>
>> 2. The local power company told me a couple of years ago that the code
>> around here anyway no longer requires installation of a ground rod at the
>> Main for a new house. What gives here?
>>
>> 73,
>> John, W3ULS
>>
>> _______________________________________________
>> TenTec mailing list
>>
TenTec@contesting.com<mailto:TenTec@contesting.com<mailto:TenTec@contesting.com<mailto:TenTec@contesting.com>>
>>
http://lists.contesting.com/mailman/listinfo/tentec<http://lists.contesting.com/mailman/listinfo/tentec<http://lists.contesting.com/mailman/listinfo/tentec<http://lists.contesting.com/mailman/listinfo/tentec>>
>
> _______________________________________________
> TenTec mailing list
>
TenTec@contesting.com<mailto:TenTec@contesting.com<mailto:TenTec@contesting.com<mailto:TenTec@contesting.com>>
>
http://lists.contesting.com/mailman/listinfo/tentec<http://lists.contesting.com/mailman/listinfo/tentec<http://lists.contesting.com/mailman/listinfo/tentec<http://lists.contesting.com/mailman/listinfo/tentec>>
_______________________________________________
TenTec mailing list
TenTec@contesting.com<mailto:TenTec@contesting.com<mailto:TenTec@contesting.com<mailto:TenTec@contesting.com>>
http://lists.contesting.com/mailman/listinfo/tentec<http://lists.contesting.com/mailman/listinfo/tentec<http://lists.contesting.com/mailman/listinfo/tentec<http://lists.contesting.com/mailman/listinfo/tentec>>
_______________________________________________
TenTec mailing list
TenTec@contesting.com<mailto:TenTec@contesting.com>
http://lists.contesting.com/mailman/listinfo/tentec<http://lists.contesting.com/mailman/listinfo/tentec>
_______________________________________________
TenTec mailing list
TenTec@contesting.com
http://lists.contesting.com/mailman/listinfo/tentec
|