Not quite. What must happen at the "Main Panel" is the bond between Neutral and Equipment Ground. That bond MUST be done where power enters the building, and it MUST be the ONLY connection between Neutral and Ground anywhere in the system. There must also be an Earth Connection (that is, a driven rod) at that point. ANY building can have as many EARTH connections as you like, and they can be connected to the "Green Wire" ANYWHERE you like, but they MUST all be bonded together.

"Equipment Ground" in the context of power systems is the steel enclosures of electrical panels, and of the "Green Wire" throughout the building.

73, Jim K9YC

On Tue,10/4/2016 12:28 PM, Roger (K8RI) wrote:
I think we're caught in semantics and interpretations. Jim (K9YC) has the correct interpretation, BUT as he says, it' the GROUNDS that are all tied together. I believe Panels and sub panels are grounded ONLY at the main panel. Sub panels have their grounds run to the main panel which is the only ground for the panels