Re: [TowerTalk] ground rod depth problem - and understanding ground rods

To: towertalk@contesting.com
Subject: Re: [TowerTalk] ground rod depth problem - and understanding ground rods
From: Jim Lux <jimlux@earthlink.net>
Date: Thu, 15 Nov 2012 04:59:37 -0800
List-post: <towertalk@contesting.com">mailto:towertalk@contesting.com>
On 11/14/12 9:12 PM, K4SAV wrote:
Jim, I think maybe you misunderstood the reason for my questions.  I
wasn't asking what the rules and regulations say.  I have that data
already.  I'm not constructing anything and want to know what to do.  I
have done that already and it has proven to work very well for many
strikes, with no damage so far.  It's the basis for some of the
regulations I wanted to know more about.

For NEC and NFPA 780, you can find the committee discussions where they propose changes to the code, and in those the theory and experiment to justify the changes get mentioned, although for the grounding electrode thing, I suspect it's old enough that it's not online.


The IEEE docs I cited have a lot of the theory and data that you're looking for. What's not in there is probably in the references for those docs.




 Maybe those regulations are
based on experimental data, I'm not sure but I suspect they are, however
I would think by now some have tried to make some sense of them
analytically.

That's in the IEEE docs.. both the analytical stuff and the experimental data.



 Anyone that wants to write some software to analyze some
of this stuff is going to have to understand the mechanisms.  I was
looking for that kind of information (not that I'm developing software,
but I'm very curious).  Grounding regulations don't describe the
mechanism of ground rod underground plasma, when it exists, and what
that does to the impedance of a ground rod.   Dave Robbins gave some
excellent data references to help with that understanding.  Thanks Dave.


You're right.. something like the NEC doesn't describe mechanisms and theory (although the NEC handbook often has additional explanations beyond what's in the straight code).

However, the IEEE docs *do* talk about what you're looking for.



Then the thought of encasing a ground rod in concrete came up, and I
don't think I have ever heard of anyone doing that.  Ufer grounds are
not exactly the same thing.  Rules for Ufer grounding aren't very
similar.

Oh... you're talking about taking a standard 10 foot rod and encasing the required buried 8 feet in concrete? That's not a Concrete Encased Grounding Electrode (what NEC calls it) or Ufer (what everyone else calls it).

The actual construction of a CEGR/Ufer (they are the same thing) has a fair amount of variability: the code has a "minimum", but in practice people build all sorts of things with varying lengths of wire and varying whether you use a copper wire or use the rebar or whatever. There's some IEEE journal papers out there which I can't remember off the top of my head where people built various kinds of Ufers and tested them. For instance, there's a whole discussion about whether the rebar has to be one continuous piece, or whether it can be sections, so someone went out and measured a bunch of cases. There's also some papers where steel columns bolted to the foundation slab were tested.

The way I find them is by starting with the references in the IEEE 1100 doc (because it's most up to date), and then working my way back through their references, etc. A lot of the work was done in the 60s and 70s, as I recall. IEEE Xplore access is probably a necessity for finding it all.


As far as modeling goes, there are papers out there where people use NEC (the antenna modeling code) to model lightning strokes and the victim structure (for induced currents and such). They run the NEC model at a whole raft of frequencies to get the transfer function vs frequency. Then, they take the Fourier transform of the lightning current waveform, run that through the model, then transform the victim current and voltage spectrum back to time domain.

There are a fair number of papers on lightning propagation within soil and rock, as well. This is a topic of some concern for mining and drilling. I don't recall if J.R. Wait wrote any papers on this, but since he probably wrote hundreds of papers on EM propagation in soil, it's a good bet.


 I know some use bentonite around a ground rod but what would
happen if someone used only one ground rod encased in concrete as the
ground for a tower?  Yeah that's probably dumb, but what would happen?

It would work.  No worse than the same rod just driven into the soil.

Would it explode?

Not likely.

 A strike can go right thru a concrete wall.  What's
the difference? (It also goes right thru many other building materials,
including tile, if those are in the path where the strike wants to go.)
There doesn't seem to be any rules for this kind of grounding, or any
data or description to help understand what will happen.  I can guess
what would happen, but I would rather not.


Spark propagation is a very, very complex topic, particularly when talking about through dielectrics. It's complex just going through air. I would suggest Bazelyan and Raizer "Spark Discharge" as one really good reference.

The book by Rakov and Uman on lightning is also a really good source of information. They might be a good place to start to look for references on "lightning effects".
http://books.google.com/books/about/Lightning.html?id=TuMa5lAa3RAC

Uman's book on "The Lightning Discharge" is probably work looking at.

His book on The Art and Science of Lightning Protection is also worth looking at

http://books.google.com/books?id=KO7fVcqispQC&source=gbs_similarbooks


And I agree that the way the ground connections are made is the most
important part of a grounding system, but that subject is easy to
understand, and not so difficult to analyze.

I realize most people don't ask these kind of questions.  As long as
they know what to do to solve the problems, most don't care how it
works.  Guess I'm just different.



Curiosity is good..

There's quite a bit of literature out there.. You just need to get started.

If you had to buy a first book on lightning, I'd get the $12 Dover press edition of Uman's Lightning

 http://www.amazon.com/Lightning-Dover-Books-Physics-Martin/dp/0486645754



Jerry, K4SAV

_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk


_______________________________________________



_______________________________________________
TowerTalk mailing list
TowerTalk@contesting.com
http://lists.contesting.com/mailman/listinfo/towertalk

<Prev in Thread] Current Thread [Next in Thread>