[Amps] oil-filled capacitor operating position

Patrick A. Thompson Sr. wa4tukhr at comcast.net
Mon Mar 1 21:29:54 EST 2004


As far as operating position, I would try to find the manufacturer's
recommendation.  For a clue into what modern types might be capable of see
http://www.plasticcapacitors.com/. The LK series will operate in any
position but I have only seen them used with the terminals up.

My personal preference would be to mount the terminals up because the
terminal area is the most probable leakage area.

Your second question is easier.  The two caps can be paralleled if you do
not exceed the rating of either.  Don't exceed the voltage rating of either
unit and don't exceed the ripple current of either unit. In practice, you
won't have to worry about anything but the voltage rating of the lowest
rated unit. The capacity is simply added together.

Pat
wa4tuk

-----Original Message-----
From: amps-bounces at contesting.com [mailto:amps-bounces at contesting.com]On
Behalf Of ka1xo at juno.com
Sent: Sunday, February 29, 2004 8:13 PM
To: amps at contesting.com
Subject: [Amps] oil-filled capacitor operating position



Gents,

What can you tell me about oil-filled capacitors in the 20 to 40 uF range,
eith a DC working voltage of 3 to 5 KV, on the subject of
operating position and being paralleled?

Do large cans need to be operated only with the ceramic insulators in the up
position?

Are two cans able to be paralleled for greater capacity if their ratings are
not exactly the same?

Thanks.

Hal