[Amps] 230v wiring question
Robert Bonner
rbonner at qro.com
Wed Apr 25 11:16:20 EDT 2007
Well here's more bad advice. SO stop it.
YOU DON'T NEED three conductors plus ground for a 220 Circuit to power your
amplifier.
UNLESS you live in some wacked out community that requires a neutral above
and beyond NEC.
You cannot terminate a white wire to ground inside a piece of equipment. It
is not a ground it is a neutral so on a TL-922 there is NO PLACE FOR A
NEUTRAL.
The reason your STOVE has 4 wires (3 conductors + ground) is it has a
neutral to run for the 120V outlets on the backsplash, it's called a
MULTI-WIRE connection. It is a special application. It has a neutral buss
inside. It runs on 120V and 220V.
Walk into home depot and look at available 220 outlets & Plugs you will see
all sorts of them for different installations, 3 and 4 wire.
He needs only his nice run of 12/2 and a 2 pole 20 amp breaker, and a 20 amp
220 outlet and a bunch of NM connectors and a box... a way to blow holes in
floor joices a few staples and a roll of black tape... Nothing more. There
needs to be no more discussion, no more bad or half baked advice, this has
been covered 62,000 times here and every time all the amateur electricians
come out to play.
I came across a note on BOB VILA'S website and it said, YOU BEST CALL AN
ELECTRICIAN, WORKING IN A SERVICE PANEL IS DANGEROUS.
http://www.naffainc.com/x/CB2/Elect/Romex.htm
Here's all about Romex.
Maybe it's time to actually study the NEC for a while before giving wiring
advice???? Slap Slap SLAP
BOB DD
-----Original Message-----
From: amps-bounces at contesting.com [mailto:amps-bounces at contesting.com] On
Behalf Of Clint Talmadge
Sent: Wednesday, April 25, 2007 7:57 AM
To: Mike McCarthy, W1NR; Jim Brown
Cc: amps at contesting.com
Subject: Re: [Amps] 230v wiring question
You will need 12/3 (which is 3 #12 wires & a separate ground) to run a 220V
circuit.
Black and Red for the Hot wires. White for the Neutral and the bare (or
Green) for the Ground.
The Breaker will determine the gauge. If you install a 20 Amp breaker, you
may run 12 Gauge. A 30 Amp Breaker necessitates 10 Gauge wire. Regardless
of which gauge you run, you can then terminate in a 15 Amp or a 20 Amp
outlet in the shack.
Clint - W5CPT
----- Original Message -----
From: Mike McCarthy, W1NR
To: Jim Brown
Cc: amps at contesting.com
Sent: Tuesday, April 24, 2007 2:23 PM
Subject: Re: [Amps] 230v wiring question
Jim Brown wrote:
> On Tue, 24 Apr 2007 12:24:45 -0500, Ken Bessler wrote:
>
>> Is 12/2 enough or will I see voltage drops
>
> #12 is just fine. It's rated for 20A, and there will be relatively
> little IR drop in such a short length.
>
> You MUST, however, pull a dedicated safety ground (green wire) with
> that line, and connect it to the third (round) pin on the outlet and
> to the ground bus in the breaker panel.
>
> 73,
>
> Jim Brown K9YC
>
>
> _______________________________________________
> Amps mailing list
> Amps at contesting.com
> http://lists.contesting.com/mailman/listinfo/amps
>
>
If it's 12/2 with ground (and most Romex type cable is) a seperate
ground is not required. The one in the jacket will suffice.
Mike, W1NR
_______________________________________________
Amps mailing list
Amps at contesting.com
http://lists.contesting.com/mailman/listinfo/amps
_______________________________________________
Amps mailing list
Amps at contesting.com
http://lists.contesting.com/mailman/listinfo/amps
More information about the Amps
mailing list