You should not change the outlets. NEMA 5-20P plugs come installed only on equipment drawing just under 15 amperes up to 20 amperes. If the equipment draws this much current, it should have a dedicated circuit. Using NEMA 5-20R receptacles for general purpose outlets invites you to easily overload the circuit. All you have to do is plug in two items using this configuration.
Jim Smith, EE
KQ6UV
--- On Sun, 8/9/09, Jim Brown <jim at audiosystemsgroup.com> wrote:
From: Jim Brown <jim at audiosystemsgroup.com>
Subject: Re: [Amps] 240V Outlet
To: "AMPS List" <amps at contesting.com>
Date: Sunday, August 9, 2009, 9:49 PM
On Sun, 09 Aug 2009 19:43:47 -0400, David C. Hallam wrote:
>OK, let me ask a question here. All of my breaker are 15A. Can I
>replace any of them with 20A breakers. Wiring is 12/2 with ground.
Yes, if the ground is also #12 or larger. You can (and should) also
change the outlets.