[Amps] FW: Bridging 120v loads across HV primary windings

Ron McCurdy firemonitor at cox.net
Wed Jun 2 09:19:05 PDT 2010


Jim,

I've been engineering electrical systems since 1962.  You are wrong.  He
must ground the tap where he gets the "neutral" and provide some type of
fuse or circuit breaker protection on the "hot".  Otherwise, if he
accidentally gets the hot grounded to something, there will be an arc until
someone runs to shut off the power to the transformer...it won't trip til
someone is fried.

Wouldn't want that on my conscience!

Ron,  KE5QDA

-----Original Message-----
From: amps-bounces at contesting.com [mailto:amps-bounces at contesting.com] On
Behalf Of Jim Brown
Sent: Tuesday, June 01, 2010 1:36 PM
To: AMPS List
Subject: Re: [Amps] Bridging 120v loads across HV primary windings

On Sun, 30 May 2010 14:34:35 -0400, Martin Flynn wrote:

>Vic,
>Run the 4 wire circuit and call it a day.    I ran this very issue by a 
>licensed master electrician on Friday.  

>Direct quote: "If any portion of the load is 120 volt, you need a 
>neutral.  If you are hell-bent on a 2 wire + ground supply, get a 208 
>volt fan and appropriately tapped transformer"

Your licensed master electrican was WRONG. It is entirely legal, and 
entirely proper from an engineering point of view to place a 120V load 
across half of a center tapped transformer as long as that load is center 
tap is not grounded. 

73,

Jim Brown K9YC


_______________________________________________
Amps mailing list
Amps at contesting.com
http://lists.contesting.com/mailman/listinfo/amps



More information about the Amps mailing list