Tim Groat tcgroat at earthlink.net
Wed Jul 28 00:12:32 EDT 2004


GFCIs had a (rescinded) immunity standard, NEMA PP1-86 
<http://www.nema.org/index_nema.cfm/563/?type=standard&pageid=7D30F99E-C55A-4933-B2CC37A5D63EAF9F&node=608>. 
This standard was much different from the IEC conducted immunity standards. 
It was a differential-mode test at 10-400MHz, 0.5Vrms, CW, 50 ohms 
(compared to common-mode, 0.15-80MHz, 3Vrms carrier, 80% AM at 1kHz, 150 
ohms per the IEC "generic" immunity test). The GFCI was tested without 
loading, and was expected to operate normally in the presence of RF (no 
nuisance trip, trip as specified when leakage exists).

With the 10MHz low frequency limit, you can see how the low bands could be 
troublesome. But it was better than no standard at all.

73,
--Tim (KR0U)

>"Michael Tope" <W4EF at dellroy.com>:
>
>I haven't had any GFI's fail, Jim at least none that I have been able
>to positively correlate with RFI (I had one fail in the kitchen, but I am 
>not positive that it was RFI induced). I did, however, have problems with 
>the GFI in our master bathroom tripping when I woudl operate 80 and 160 
>meters with my amplifier.